HI Team,
Can i change the Modbus TCP/IP device address for PM5340? is the BACNET device address can be use for modbus device addreess if BACNET is disabled?
BR,
SESA427078
Link copied. Please paste this link to share this article on your social media post.
Hello @sesa427078_brid
The Modbus unit ID is fixed as 255 and it cannot be changed since the PM5340 is standalone Modbus TCP device. The default BACnet device ID will be the last 3 digit of PM5340 meter serial number and it cab be changed by the user if required.
Regards,
Ramasamy N
Link copied. Please paste this link to share this article on your social media post.
Hello @Ramasamy_N ,
Do you know if possible to change the modbus device address for modbus TCP on PM5340 meters?
@sesa427078_brid , the BACNET and modbus protocols are completely separate and do not share any information. It may be possible for a device to be configured with same ID numbers in both protocols but this would be 2 settings, device ID in Modbus and Device ID in BACNET.
Regards,
Charles
Link copied. Please paste this link to share this article on your social media post.
Hello @sesa427078_brid
The Modbus unit ID is fixed as 255 and it cannot be changed since the PM5340 is standalone Modbus TCP device. The default BACnet device ID will be the last 3 digit of PM5340 meter serial number and it cab be changed by the user if required.
Regards,
Ramasamy N
Link copied. Please paste this link to share this article on your social media post.
Hello @Ramasamy_N
"The Modbus unit ID is fixed as 255 and it can be changed ..."
I have not found a way to change this, maybe you have a typo? you mean it cannot be changed?
Link copied. Please paste this link to share this article on your social media post.
Hello @diego.pedraza
Sorry, it was typo error. The Modbus unit ID can not be changed in PM5340 meter, since it is standalone TCP device.
The meter which supports gateway feature can change the unit ID.
Regards,
Ramasamy N
Link copied. Please paste this link to share this article on your social media post.
That makes sense its 255 since our IFE modules that talk to the breakers also use 255 as the default Modbus address and cannot be changed either