Continue
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • My Subscriptions
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

PM5100 Aux Power Source being the same as load

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • PM5100 Aux Power Source being the same as load
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Charles_Murison Champion
582
Mehran_Mehrnia
Mehran_Mehrnia Champion
216
Ramasamy_N
Ramasamy_N Champion
117
View All

Recommended Forums

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Start a Topic
Solved
foolserrand
foolserrand
Contributor

Posted: ‎2025-02-03 02:54 PM

0 Likes
5
1427
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-02-03 02:54 PM

PM5100 Aux Power Source being the same as load

The manual specifies that the Aux power supply, must not be connected to the load side of the measured circuit.

We do not have an auxiliary supply but wish to make use of the PM5100 on a single phase supply.

Although labelled as Aux power supply, my understanding is this is the only way of powering the unit?

What is the result of connecting AUX power supply input to the Voltage inputs? without which I assume the unit will display zero values.

Labels
  • Labels:
  • PM5000
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
geir_eas_no_bfo
geir_eas_no_bfo
Troubleshooter

Posted: ‎2025-02-05 09:31 AM

0 Likes
0
1359
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-02-05 09:31 AM

Yes of course you can power it from same single load, and there is no other consequences than MID requirements not met. 

BR

GIA

See Answer In Context

Reply
foolserrand
foolserrand
Contributor

Posted: ‎2025-02-05 03:54 PM

0 Likes
0
1326
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-02-05 03:54 PM

Conflicting advice here, ranging from measurement interference and accuracy to being simply a non compliance issue for MID.

I conclude that for my purposes any suggested inaccuracy would be minimal (if at all) and that it will not harm the unit which was my primary concern.

See Answer In Context

Reply
Replies 5
Mehran_Mehrnia
Mehran_Mehrnia Champion
Champion

Posted: ‎2025-02-04 08:14 AM . Last Modified: ‎2025-02-04 08:14 AM

0 Likes
0
1406
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-02-04 08:14 AM

Hi @foolserrand 

 

If this is about the PM5110 as a MID-compliant meter, it meets the requirements that establish standards for the accuracy and performance of measuring instruments used for billing purposes.

 

Given that the meter can be powered up with line voltage in the range of 100-277 V L-N AC or 100-415 V L-L AC, as mentioned in the user guide, the auxiliary power supply of the meter must be connected in a way that ensures uninterrupted operation in situations where any one or two phases of the measured circuit become de-energized.

 

Best Regards,

-Mehran

L3 Expert Advanced metering

Reply
foolserrand
foolserrand
Contributor

Posted: ‎2025-02-04 08:20 AM

0 Likes
1
1381
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-02-04 08:20 AM

Thank you, I understand the desirability of an uninterrupted supply.

However, as stated we do not have such available and have no requirement for monitoring while de-energized.

What are the consequences of powering the PM5110 from the same single phase load?

Reply
geir_eas_no_bfo
geir_eas_no_bfo
Troubleshooter

Posted: ‎2025-02-05 09:31 AM

0 Likes
0
1359
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-02-05 09:31 AM

Yes of course you can power it from same single load, and there is no other consequences than MID requirements not met. 

BR

GIA

Reply
Mehran_Mehrnia
Mehran_Mehrnia Champion
Champion

Posted: ‎2025-02-05 09:46 AM

1 Like
0
1359
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-02-05 09:46 AM

Hi @foolserrand 

 

You're welcome.

 

The meter itself does not care which source has powered it up, however in MID (Measurement Instrument Directive) meters, the auxiliary power supply must not be connected to the load side of the measured circuit to ensure accurate measurements cause it could create interference in the measurement, affecting the accuracy of the readings by introducing additional voltage or current from the auxiliary supply.

 

MID regulations require that the auxiliary power supply be isolated from the load side to maintain compliance with standards and ensure reliable operation of the meter.

 

Best Regards,

-Mehran

L3 Expert Advanced metering

Reply
foolserrand
foolserrand
Contributor

Posted: ‎2025-02-05 03:54 PM

0 Likes
0
1326
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-02-05 03:54 PM

Conflicting advice here, ranging from measurement interference and accuracy to being simply a non compliance issue for MID.

I conclude that for my purposes any suggested inaccuracy would be minimal (if at all) and that it will not harm the unit which was my primary concern.

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore