Hello,
We use DO1 count of PM5320 to outpu of energy pulsing.
What value does the counter roll over by?
[DO1 count]
Digital Outputs Status
Base Unit - Digital Output DO1
Count (Modbus Register 9675 INT32U)
The register is INT32U, the maximum value of INT32U is 4,294,967,295 (=2^32-1).
Thus I think the roll over value is also 4,294,967,295 (=2^32-1).
Is my understanding correct?
Thank you.
Accepted Solutions
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Hello,
Yes, you are right.
The DO count and on time counters will be roll over after 4,294,967,295 counts.
Regards,
Ramasamy N