Continue
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • My Subscriptions
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

How many concurrent Modbus TCP connections are allowed on the PM5000 series meters with Ethernet?

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • How many concurrent Modbus TCP connections are allowed on the PM5000 series meters with Ethernet?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Charles_Murison Champion
582
Mehran_Mehrnia
Mehran_Mehrnia Champion
217
Ramasamy_N
Ramasamy_N Champion
117
View All

Recommended Forums

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Start a Topic
Solved
JamesAZZO
JamesAZZO
Leader

Posted: ‎2014-02-06 09:07 PM

0 Likes
7
4312
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2014-02-06 09:07 PM

How many concurrent Modbus TCP connections are allowed on the PM5000 series meters with Ethernet?

How many concurrent Modbus TCP connections are allowed on the PM5000 series meters with Ethernet?

I really hope more than 1 client! 🙂

Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
sesa19908
sesa19908 Leader
Leader

Posted: ‎2014-02-10 08:25 AM

1 Like
5
4090
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2014-02-10 08:25 AM

James,

The PM5560 supports 128 concurrent TCP/IP Ethernet connections, these are used for HTTP, FTP, Modbus TCP and other protocols.

The maximum concurrent HTTP connections is 20.

See Answer In Context

Reply
shreesha_pandit
shreesha_pandit Leader
Leader

Posted: ‎2014-02-12 07:43 PM

0 Likes
2
4090
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2014-02-12 07:43 PM

James

PM5320/40 meters supports 4 concurrent Modbus TCP/IP connections.

See Answer In Context

Reply
Charles_Murison
Charles_Murison Champion
Champion

Posted: ‎2019-04-22 08:45 AM

1 Like
0
4078
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-04-22 08:45 AM

Default is 32 connections

L4 Prime for Advanced metering and Utilities

See Answer In Context

Reply
Replies 7
JamesAZZO
JamesAZZO
Leader

Posted: ‎2014-02-08 05:16 AM

0 Likes
6
4090
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2014-02-08 05:16 AM

?

Reply
sesa19908
sesa19908 Leader
Leader

Posted: ‎2014-02-10 08:25 AM

1 Like
5
4090
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2014-02-10 08:25 AM

James,

The PM5560 supports 128 concurrent TCP/IP Ethernet connections, these are used for HTTP, FTP, Modbus TCP and other protocols.

The maximum concurrent HTTP connections is 20.

Reply
JamesAZZO
JamesAZZO
Leader

Posted: ‎2014-02-10 04:27 PM

0 Likes
4
4090
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2014-02-10 04:27 PM

That's great news! Can you be more specific about the PM5320 and PM5340 with Ethernet? You mention the PM5560, but what about the others?

What's the maximum Modbus TCP connections?

Reply
sesa19908
sesa19908 Leader
Leader

Posted: ‎2014-02-11 07:08 AM

1 Like
0
4090
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2014-02-11 07:08 AM

I will let Shreesha Pandith respond about the PM5320 and PM5340, he is closer to that

development.

From: James DiLiberto <powersolutionscommunity-admin@powersolutionscommunity.hosted.jivesoftware.com>

To: Marcelo Perez <marcelo.perez@schneider-electric.com>,

Date: 02/10/2014 06:28 PM

Subject: Re: - How many concurrent Modbus TCP connections are allowed on the PM5000

series meters with Ethernet?

Solutions Expert Community

How many concurrent Modbus TCP connections are allowed on the PM5000 series meters with

Ethernet?

reply from James DiLiberto in Power Monitoring Hardware - View the full discussion

That's great news! Can you be more specific about the PM5320 and PM5340 with Ethernet? You

mention the PM5560, but what about the others?

What's the maximum Modbus TCP connections?

Reply to this message by replying to this email, or go to the message on Solutions Expert

Community

Start a new discussion in Power Monitoring Hardware by email or at Solutions Expert Community

Following How many concurrent Modbus TCP connections are allowed on the PM5000 series meters

with Ethernet? in these streams: Inbox

Reply
shreesha_pandit
shreesha_pandit Leader
Leader

Posted: ‎2014-02-12 07:43 PM

0 Likes
2
4090
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2014-02-12 07:43 PM

James

PM5320/40 meters supports 4 concurrent Modbus TCP/IP connections.

Reply
Eddic
Eddic
Explorer

Posted: ‎2019-04-21 11:46 PM

0 Likes
1
4082
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-04-21 11:46 PM

Hi, How about the PM8ECC module ?

Reply
Charles_Murison
Charles_Murison Champion
Champion

Posted: ‎2019-04-22 08:45 AM

1 Like
0
4078
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-04-22 08:45 AM

Default is 32 connections

L4 Prime for Advanced metering and Utilities
Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore