Is there a logging template available for PM5000 meters that offers detailed logging (mean/high/low) values, similar to the PME PM8000 templates?
The PM5000 profile supports the objects in their Modbus profile, indicating that it should be possible to obtain these values.
Is there a template that provides logging for PM5000 meters for detailed logging (mean/high/low) values?
Could we confirm if such a template exists?
Link copied. Please paste this link to share this article on your social media post.
Hi @Evren
PM5000 series depending on the meter's type(PM5100, PM5300, PM5500, PM5600 and PM5700) have limited Data Recorders(up to 4) and Data logging sources up to 16 parameters with fixed available sources and it is not like PM8000 with user definable Data Recorders and data logs sources.
Regarding Min/Max values, meter only updates and saves these min/max quantities in non-volatile memory when the readings reach their lowest or highest value, and they cannot be recorded with configurable interval.
PM5000 Datasheet:
https://www.se.com/au/en/download/document/PLSED310052EN_Web/
Best Regards,
-Mehran
Expert Technical Support Specialist
Link copied. Please paste this link to share this article on your social media post.
Hi @Evren
PM5000 series depending on the meter's type(PM5100, PM5300, PM5500, PM5600 and PM5700) have limited Data Recorders(up to 4) and Data logging sources up to 16 parameters with fixed available sources and it is not like PM8000 with user definable Data Recorders and data logs sources.
Regarding Min/Max values, meter only updates and saves these min/max quantities in non-volatile memory when the readings reach their lowest or highest value, and they cannot be recorded with configurable interval.
PM5000 Datasheet:
https://www.se.com/au/en/download/document/PLSED310052EN_Web/
Best Regards,
-Mehran
Expert Technical Support Specialist
Link copied. Please paste this link to share this article on your social media post.
Hello @Evren
I am not sure about the template created for (mean/high/low) values before.
However you can create PC based logs using the Modbus registers stating from 27218 (min) and 27694 (max).
Please note this register will overwrite only when new min or max value measured.
Regards,
Ramasamy N