Metering & Power Quality
Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.
Link copied. Please paste this link to share this article on your social media post.
Hi Everyone,
my customer have PM5000 series which have wrench icon on next left top power meter display (on normal condition show black square), i check on menu diagnostic > status show code 0081 Hex (on normal condition show "OK")
FAQ told "0081" stand for "Back up Ram/ Vbat Fail"
https://www.se.com/sg/en/faqs/FA272968/
why this code occur ? and how to repair it? or the power meter must be replaced ?
Link copied. Please paste this link to share this article on your social media post.
Hi @sesa738450
When the wrench symbol appears in the top left corner of the display with the error code 0081 hex under the diagnostic page, it's very likely that the meter's battery is dead. Unfortunately, the battery is not field replaceable.
0081 : Back up Ram/ Vbat Fail
Best Regards,
-Mehran
L3 Expert Advanced metering
Link copied. Please paste this link to share this article on your social media post.
Well, i will ask customer to check warranty. Thanks for your answer @Mehran_Mehrnia
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.