Is it feasible to reset peak demand values on a PM2120 power meter through Modbus commands?
Link copied. Please paste this link to share this article on your social media post.
As the primary programmer of ION Setup, I can tell you that this will require multiple steps to be performed by any software which wishes to do this operation as this isn't as straightforward as doing a single Modbus transaction. This would likely require significant work on the EBO software development team to perform any type of meter resets.
Link copied. Please paste this link to share this article on your social media post.
Hi @Anuradha
It better to ask in the meters' forum: Metering & Power Quality - Schneider Electric Community (se.com)
Thanks,
Mahmoud
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Hi @Anuradha
Yes, you can reset the peak demand values by sending the Modbus command number 2015. The default password will be 0 for reset the demand values.
Or use the ION setup to reset the peak demand values.
Regards,
Ramasamy N
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
I am not sure in EBO, You can check for the Modbus write multiple register function (FC16) to add this Modbus command in EBO.
Link copied. Please paste this link to share this article on your social media post.
Hi @Ramasamy_N ,
This is a common issue and we need to know how the demand reset can be done through Modbus RTU. Mostly we are using EBO to do this. Please guide us to do these commands through EBO.
Link copied. Please paste this link to share this article on your social media post.
Hello @ajith_iqsystems,
Not all people know all products from Schneider. To write commands to the PM2100 devices takes multiple steps. People who support meters likely do not know details about other Schneider Software products. Does EBO support multiple step writes to a device?
Regards,
Charles
Link copied. Please paste this link to share this article on your social media post.
You can connect with country tech support team for this EBO query, they will be able to guide you.
Regards,
Ramasamy N
Link copied. Please paste this link to share this article on your social media post.
As the primary programmer of ION Setup, I can tell you that this will require multiple steps to be performed by any software which wishes to do this operation as this isn't as straightforward as doing a single Modbus transaction. This would likely require significant work on the EBO software development team to perform any type of meter resets.