Hi all,
Couple of things,
Has anyone taken a Modbus rtu bus of PM5330's into a Modbus rtu to bacnet ip gateway ?
- Are points auto transposed to bacnet objects, and little modbus config required ?
- The naming all comes through intact ?
- Changeover of values ( kilowatts to Megawatts ) requires no config
Thanks in advance,
Rich
Authentication Failed.
- Authentication Ticket Mismatched, failed authentication.
Accepted Solutions
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Hello GIA,
The gateway option in PM5563 supported only for Modbus protocol. We can not use as BACnet gateway.
However, the BMS controller like SE Automation server (https://www.se.com/in/en/download/document/03-14020-en/) supports the Modbus serial port to read the data from NSX Micrologic and PM5330 and view the data in the BMS system.
Regards,
Ramasamy N
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Hello @DickyGray
Never tried to convert the PM5330 Modbus RTU to the BACnet IP objects, You can explore the gaetway manual.
However PM5340 supports BACnet IP protocol. The list of supported objects are listed in PM5300 user manual.
Regards,
Ramasamy N
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Hi,
Schneider has limited productes for bacnet and reading NSX Micrologic.
Can we use a PM5563 as a Bacnet gateway for NSX devices connected with RS485?
BR
GIA
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Hello GIA,
The gateway option in PM5563 supported only for Modbus protocol. We can not use as BACnet gateway.
However, the BMS controller like SE Automation server (https://www.se.com/in/en/download/document/03-14020-en/) supports the Modbus serial port to read the data from NSX Micrologic and PM5330 and view the data in the BMS system.
Regards,
Ramasamy N
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Hi, thanks for the clarifictation.
I will ask my SE-representative why this product is not supported in Norway.
BR
GIA