Hi, Reaching out regarding an error message and filter malfunction for a PCSn060Y4CH00.
I have upgraded firmware to AccuSine PCSn Active Harmonic Filter Firmware Upgrade v002.002.004 (CB.v2.3.0). See attached error message.
What could be the issue on the filter??
/Daniel
Link copied. Please paste this link to share this article on your social media post.
Hello Daniel,
Hope you are doing good.
It is good that you have upgraded the PCSn with latest firmware.
In addition i recommend you to login to CERT mode and got to Unit setting---> Advance setting-->Sensor startup Check- Turn it to Off.
Then i recommend to do Integrity test.
Integrity Test, provides a means to verify the unit or system is operational.
I have attache the PCSn User manual, refer Page 34 and 44 for more details.
Even after this if you are still facing the same issue, i re-commend to raise a BFO Case, here below is the link, where you can find your region(country) and select the respective CCC and log a BFO Case.
https://www.se.com/ww/en/work/support/country-selector/contact-us.jsp
Regards
Link copied. Please paste this link to share this article on your social media post.
Hello Daniel,
Hope you are doing good.
It is good that you have upgraded the PCSn with latest firmware.
In addition i recommend you to login to CERT mode and got to Unit setting---> Advance setting-->Sensor startup Check- Turn it to Off.
Then i recommend to do Integrity test.
Integrity Test, provides a means to verify the unit or system is operational.
I have attache the PCSn User manual, refer Page 34 and 44 for more details.
Even after this if you are still facing the same issue, i re-commend to raise a BFO Case, here below is the link, where you can find your region(country) and select the respective CCC and log a BFO Case.
https://www.se.com/ww/en/work/support/country-selector/contact-us.jsp
Regards