Metering & Power Quality
Hi, Reaching out regarding an error message and filter malfunction for a PCSn060Y4CH00.
I have upgraded firmware to AccuSine PCSn Active Harmonic Filter Firmware Upgrade v002.002.004 (CB.v2.3.0). See attached error message.
What could be the issue on the filter??
/Daniel
Hello Daniel,
Hope you are doing good.
It is good that you have upgraded the PCSn with latest firmware.
In addition i recommend you to login to CERT mode and got to Unit setting---> Advance setting-->Sensor startup Check- Turn it to Off.
Then i recommend to do Integrity test.
Integrity Test, provides a means to verify the unit or system is operational.
I have attache the PCSn User manual, refer Page 34 and 44 for more details.
Even after this if you are still facing the same issue, i re-commend to raise a BFO Case, here below is the link, where you can find your region(country) and select the respective CCC and log a BFO Case.
https://www.se.com/ww/en/work/support/country-selector/contact-us.jsp
Hello Daniel,