Hi all,
Regarding PM 5330, 39056 of meter power up( control power loss) table below has alarm all the time.
Also 0 and 1 bit is repeating .
Could you please answer below questions?
1. PM5330, 39056 Meter Power Up (Control Power Loss) will be automatically restored.
How long does it take to recover automatically?
2. How do I reset it if it doesn't auto-recovery?
Authentication Failed.
- Authentication Ticket Mismatched, failed authentication.
Accepted Solutions
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Hello @Tom_Stevenson
Supaing reached directly and addressed this query.
Hello Supaing,
The meter power up alarm is factory enabled alarm which will be active all the time.
This alarm will not recover by itself at any point of time.
You can disable this meter power up alarm from the meter front display, if this alarm is not required or useful.
Regards,
Ramasamy N
Hi Ramasamy,
I really appreciated for your advice.
I have tried it. It work.
Thank for your precious help.
Best Regards
Supaing
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Hello @Tom_Stevenson
Supaing reached directly and addressed this query.
Hello Supaing,
The meter power up alarm is factory enabled alarm which will be active all the time.
This alarm will not recover by itself at any point of time.
You can disable this meter power up alarm from the meter front display, if this alarm is not required or useful.
Regards,
Ramasamy N
Hi Ramasamy,
I really appreciated for your advice.
I have tried it. It work.
Thank for your precious help.
Best Regards
Supaing