Hi Xperts,
Need advise on how to activate neutral current readings from PM5580. Do we need to provide additional CT for this requirement? If yes, which CTs would you recommend.
Thanks,
Jedz
Link copied. Please paste this link to share this article on your social media post.
Hello @jedzruiz1985 The fourth current input (I4) is used to measure current flow (In) in the neutral
conductor. This is also connected with a CT identical in electrical characteristics to the I1–I3 inputs.
Link copied. Please paste this link to share this article on your social media post.
Hello @jedzruiz1985 The fourth current input (I4) is used to measure current flow (In) in the neutral
conductor. This is also connected with a CT identical in electrical characteristics to the I1–I3 inputs.