Multiple "Ethernet Auth Ok" and "Ethernet Auth Fail" events

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • Multiple "Ethernet Auth Ok" and "Ethernet Auth Fail" events
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Picard Charles_Murison Picard
529
Mehran_Mehrnia
Admiral Mehran_Mehrnia Admiral
140
Ramasamy_N
Captain Ramasamy_N Captain
115
View All

Recommended Forums

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Start a Topic
Solved
danielbarrantes
Lieutenant JG danielbarrantes
Lieutenant JG

Posted: ‎2021-09-07 10:55 AM . Last Modified: ‎2021-09-07 11:03 AM

1 Like
3
2675
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-09-07 10:55 AM

Multiple "Ethernet Auth Ok" and "Ethernet Auth Fail" events

 

I have had some inconveniences due to a large number of events generated by various energy meters since when performing an event count at the end of the month, they present between 30,000 to 50,000 events per "Cause: Ethernet" and "Effect value: Auth Ok and Auth Fail ".

 

Initially it was thought that they were generated every time someone tried to register, however due to the large number of monthly events it is impossible that this is due to a failed authentication by a user.

 

I need to know the origin of these events so that I can attack the root cause and that they do not generate as much disk space.

 

Ejm.PNG 

Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Charles_Murison
Picard Charles_Murison Picard
Picard

Posted: ‎2021-09-21 11:37 AM

0 Likes
2
2622
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-09-21 11:37 AM

Hello @danielbarrantes ,

 

By chance, are these devices time sync'd via PME? If so this could explain some of these events. When PME sends a time sync to a meter with advanced security there are actually 2 time sync messages, one without user security information and a second with security information. Some meters will ignore the first message, others will register that message as a failed authentication.

 

Not much that can be changed inside PME at this time. The T1 device to me looks like information in some software (likely PME) is using the wrong password for User1.

 

Regards,

Charles.

L4 Prime for Advanced metering and Utilities

See Answer In Context

Tags (1)
  • Tags:
  • english
Reply
Replies 3
Charles_Murison
Picard Charles_Murison Picard
Picard

Posted: ‎2021-09-21 11:37 AM

0 Likes
2
2623
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-09-21 11:37 AM

Hello @danielbarrantes ,

 

By chance, are these devices time sync'd via PME? If so this could explain some of these events. When PME sends a time sync to a meter with advanced security there are actually 2 time sync messages, one without user security information and a second with security information. Some meters will ignore the first message, others will register that message as a failed authentication.

 

Not much that can be changed inside PME at this time. The T1 device to me looks like information in some software (likely PME) is using the wrong password for User1.

 

Regards,

Charles.

L4 Prime for Advanced metering and Utilities
Tags (1)
  • Tags:
  • english
Reply
Grant_IPACS
Commander Grant_IPACS
Commander

Posted: ‎2021-09-21 11:51 AM

0 Likes
1
2620
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-09-21 11:51 AM

Hi @Charles_Murison  and @danielbarrantes , @jerry_IPACS  and I have seen similar issues on one of our sites and thought it may be because we are not using the default meter password, is there any fix on the horizon?

 

 

Regards

Grant
Tags (1)
  • Tags:
  • english
Reply
Charles_Murison
Picard Charles_Murison Picard
Picard

Posted: ‎2021-09-21 11:54 AM

0 Likes
0
2619
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-09-21 11:54 AM

Hello @Grant_IPACS ,

 

Would need to know more details, device types, firmware versions, advanced/standard/no security/legacy security enabled or disabled, number of devices etc. Time sync is just one possible reason, more investigations would be needed to determine if this is the root cause on your system.

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities
Tags (1)
  • Tags:
  • english
Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore