Hello @dongonai ,
I believe this is from the number of digits the meter is trying to display. For example if you have a 115kv system and you are trying to display 1.xxx volts, there are too many digits for the display to show. if instead you wanted 1.xxx kV likely you would be able to display.
Regards,
Charles