Hello,
I have a device connected to AS-P using Modbus TCP. I need to read the serial number and some other values which are string type in the device.
In the Modbus Point menu when I try to add a new value I get Digital, Analog, Multibit and Multistate types, no String. If I create an internal String value, I don't know how to connect it to the Modbus TCP device.
Please advice how to proceed. I was thinking about converting each character in ASCII code and sending it as INT but I can't do it in the Modbus TCP device, so it is not an option.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
@kalatech modbus transfers data values in bits and bytes and does not have a concept of strings, and there is not a String object for Modbus in EBO.
As Strings are just byte arrays if the customer can read the raw data into a Modbus point it could possibly be input to a Script program and converted. However modbus registers can only be up to 64-bits in length. This is basically an 8 ASCII character string and to go past that you would need to implement a Modbus Batch Read Function to read a batch of strings to ensure they are grouped together. If you encounter polling/error problems etc you may run into trouble.
Link copied. Please paste this link to share this article on your social media post.
I tried to read using 64 bit number but it turned out regarding this string value the device only answers to a modbus request for 10 registers and throws exception for any bigger or smaller amount. Can you give me an example how to use Modbus batch read?