Hello,
I have a device connected to AS-P using Modbus TCP. I need to read the serial number and some other values which are string type in the device.
In the Modbus Point menu when I try to add a new value I get Digital, Analog, Multibit and Multistate types, no String. If I create an internal String value, I don't know how to connect it to the Modbus TCP device.
Please advice how to proceed. I was thinking about converting each character in ASCII code and sending it as INT but I can't do it in the Modbus TCP device, so it is not an option.
Accepted Solutions
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
@kalatech modbus transfers data values in bits and bytes and does not have a concept of strings, and there is not a String object for Modbus in EBO.
As Strings are just byte arrays if the customer can read the raw data into a Modbus point it could possibly be input to a Script program and converted. However modbus registers can only be up to 64-bits in length. This is basically an 8 ASCII character string and to go past that you would need to implement a Modbus Batch Read Function to read a batch of strings to ensure they are grouped together. If you encounter polling/error problems etc you may run into trouble.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
I tried to read using 64 bit number but it turned out regarding this string value the device only answers to a modbus request for 10 registers and throws exception for any bigger or smaller amount. Can you give me an example how to use Modbus batch read?