Continue
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • My Subscriptions
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Modbus Repeater

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • Modbus Repeater
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Charles_Murison Champion
582
Mehran_Mehrnia
Mehran_Mehrnia Champion
217
Ramasamy_N
Ramasamy_N Champion
117
View All

Recommended Forums

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2017-03-21 09:47 AM

0 Likes
3
3854
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2017-03-21 09:47 AM

Modbus Repeater

Can anybody suggest a reliable Modbus repeater, do Schneider make one ?

We are going to end up with over the 32 devices on a modbus chain (iEM3000 range) and can't get round it any other way, would a repeater be the best option ?

Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Hal_Etheridge
Hal_Etheridge Champion
Champion

Posted: ‎2017-03-21 01:02 PM

2 Likes
1
3782
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2017-03-21 01:02 PM

If the number of the devices is just over 32 and the RS485 wire length is not near the maximum I would try it as is.

Most RS485 transceivers produced in the last 20 years are actually 1/4 (or better) loading of the standard so putting a few more on the loop should be fine.  This is assuming the RS485 is properly terminated etc of course.

Remember that just because electrically it may work does not mean that the software can get the data out of the device efficiently.  The more devices you have on the loop means ever slower polling intervals.  With 32+ devices on a loop you are looking at a fastest update period possible of at least 10-15 seconds and likely very significantly larger depending on what is being requested.

This configuration is NOT recommended if there is any other possible solution.  Please consider splitting this large loop up.  It will help prevent performance problems from occurring in the future which will likely be more expensive to fix then than making the change now.

See Answer In Context

Reply
Replies 3
Hal_Etheridge
Hal_Etheridge Champion
Champion

Posted: ‎2017-03-21 01:02 PM

2 Likes
1
3782
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2017-03-21 01:02 PM

If the number of the devices is just over 32 and the RS485 wire length is not near the maximum I would try it as is.

Most RS485 transceivers produced in the last 20 years are actually 1/4 (or better) loading of the standard so putting a few more on the loop should be fine.  This is assuming the RS485 is properly terminated etc of course.

Remember that just because electrically it may work does not mean that the software can get the data out of the device efficiently.  The more devices you have on the loop means ever slower polling intervals.  With 32+ devices on a loop you are looking at a fastest update period possible of at least 10-15 seconds and likely very significantly larger depending on what is being requested.

This configuration is NOT recommended if there is any other possible solution.  Please consider splitting this large loop up.  It will help prevent performance problems from occurring in the future which will likely be more expensive to fix then than making the change now.

Reply
Anonymous user
Not applicable

Posted: ‎2017-03-22 03:23 AM

0 Likes
0
3782
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2017-03-22 03:23 AM

Hal, hi

Yep, it's just over, in fact 35 devices on a very short chain <20M, from experience i think it will work but we need to allow for the cost of the hardware just in case.

Any suggestions for a repeater that we know works ? We are using a PM5560 as the gateway talking to 35 x iEM3155's just energy and power readings coming back to others software not under our supply (not PME either unfortunately)

Cheers

Reply
michael_franz
michael_franz
Mentor

Posted: ‎2017-03-28 01:01 PM

0 Likes
0
3783
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2017-03-28 01:01 PM

TEAM:

There are several great comments regarding devices, cable lengths with RS485.  Rules are rules but sometimes can be broken.   As devices are added to a daisy-chain the data loading on the string can cause a slow down in data acquisition. 

When simple meters without onboard logging are used this is typically not a big deal.  However if there are several software packages will be accessing devices on a single RS485 string it is important to take this into consideration.

This can happen if BMS/BAS, SCADA or Generator packages are being used besides PME.  This can cause unexpected drop outs if too many requests are being sent along this data path.

If more advanced meter with onboard logs and waveform data are involved this can also take a lot of the band width on a serial string.

Thanks,

Michael Franz

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore