Does anybody know the ION registries used to switch the digital output 1 & 2 after configuration in Designer to D01 and D02?
Thanks,
Jon
Link copied. Please paste this link to share this article on your social media post.
Now resolved, It was the external pulse tied to the modbus address 42020 for external pulse 20.
Thanks for the help,
Jon
Link copied. Please paste this link to share this article on your social media post.
Not sure what you mean by "switch", toggle the state of the output, change the label?
Second, heading is asking modbus register, question is asking ION register. There is a difference.
Link copied. Please paste this link to share this article on your social media post.
Doing Modbus writes to a ION meter is a little tricky.
You can only do writes to a set of External modules. I believe the map is fixed
You have to link an External Boolean module or an External Pulse Module to the DO Module.
It's documented "somewhere" so have a look at the Modbus doc for ION or check the Knowledge base.
Jim