How to change PM8xx data log file mode

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • How to change PM8xx data log file mode
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Picard Charles_Murison Picard
529
Mehran_Mehrnia
Admiral Mehran_Mehrnia Admiral
139
Ramasamy_N
Captain Ramasamy_N Captain
115
View All

Recommended Forums

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Metering & Power Quality
Start a Topic
Robert_Lee
Admiral Robert_Lee Admiral
Admiral

Posted: ‎2014-01-29 12:32 PM . Last Modified: ‎2020-04-22 01:52 AM

0 Likes
0
1542
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2014-01-29 12:32 PM

How to change PM8xx data log file mode

The default setup file doesn't support the modification of the data log file mode but this functionality can be manually added to the file using the following steps.

 

Using Windows Explorer, locate the ION Setup program folder (typically C:\Program Files\Schneider Electric) and go into the TABLES sub-folder.

 

Next, go into the folder for the model you wish to add the file mode to (ex. PM820).  In that folder, you will find a SETUP.CFG file which you should open using a text editor such as Notepad.

 

Locate the section for the log you wish to add.  Below is the section for Data Log #1 for the PM820.

 

[Data Log #1]

FeatureMask=0x00010000

SetupNum=3

SetupType=1

StartAddress=47002,47012

Registers=4,4

Setup1=1,7,Status

List1=0=Disable,2730=Auto-Enable,65535=Enable

Setup2=3,32,Interval

Limit2=0,1440

Setup3=7,24,Channels

ChannelOffset=3

TotalFileSize=7404

FileInfo=1,32700

 

Increase the SetupNum by 1 (In the above example, this is done by modifying the line SetupNum=3 to SetupNum=4).

 

We'll insert the FileMode after the Interval, so we need to add the following line above the Setup3 line and change that line to read Setup4 instead.

 

Setup3=2,7,File Mode

List3=0=FIFO,1=Fill and Hold

Setup4=7,24,Channels

 

The section should now look similar to the following:

 

[Data Log #1]

FeatureMask=0x00010000

SetupNum=4

SetupType=1

StartAddress=47002,47012

Registers=4,4

Setup1=1,7,Status

List1=0=Disable,2730=Auto-Enable,65535=Enable

Setup2=3,32,Interval

Limit2=0,1440

Setup3=2,7,File Mode

List3=0=FIFO,1=Fill and Hold

Setup4=7,24,Channels

ChannelOffset=3

TotalFileSize=7404

FileInfo=1,32700

 

Save the file and reopen the Data Log setup screen in ION Setup and the File Mode will now be displayed and can be changed if desired to do so.

Labels
  • Labels:
  • ION Setup
Reply
  • All forum topics
  • Previous Topic
  • Next Topic
Replies 0

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore