Meter PM5340 Current reading problem

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • Meter PM5340 Current reading problem
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Picard Charles_Murison Picard
509
Ramasamy_N
Captain Ramasamy_N Captain
115
Mehran_Mehrnia
Captain Mehran_Mehrnia Captain
113
Robert_Lee
Admiral Robert_Lee Admiral
96
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Metering & Power Quality
Youssef-asec
Crewman Youssef-asec
Crewman

Posted: ‎2025-09-10 06:03 AM

0 Likes
4
51
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-09-10 06:03 AM

Meter PM5340 Current reading problem

I have three meters from same bus 

1-PV solar 

2-Grid 

3-Outgoing

Three meters connected on ethernet switch then i am reading values through plc 

the problem is when I am reading current phase A which is Register 3000

SUM OF Current for PV Grid and Grid incomer is not equal to outgoing

so what can be the reason for that 

Labels
  • Labels:
  • PM5000
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Next Topic
Replies 4
Jesus_Diaz
Lt. Commander Jesus_Diaz Lt. Commander
Lt. Commander

Posted: ‎2025-09-10 11:04 AM

0 Likes
1
43
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-09-10 11:04 AM

Hello @Youssef-asec,

Have you measured the current of each meter using a clamp meter or multimeter and compared it to the values shown on the meters?

There could be wiring issues such as CT polarity, incorrect phase order, or an incorrectly configured CT ratio. Please ensure the installation follows the instructions provided in the installation sheet.

 

Additionally, verify that all meters are measuring the same phase consistently and that there are no loose connections or grounding issues that could affect accuracy.

 

Regards,

JD

Reply
Youssef-asec
Crewman Youssef-asec
Crewman

Posted: ‎2025-09-11 02:22 PM . Last Modified: ‎2025-09-11 02:24 PM

0 Likes
0
26
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-09-11 02:22 PM

Hello@Jesus_Diaz

thanks for your support 

CT polarity checked
phase order checked

all meters measuring the same phase 
I notice that during night when we feed from grid only everything is good

I notice also increase in harmonics of voltage when PV start feeding 
voltage harmonics is up to 20%
but when grid feed only without PV harmonics is 4% 

Reply
Jesus_Diaz
Lt. Commander Jesus_Diaz Lt. Commander
Lt. Commander

Posted: ‎2025-09-12 11:37 AM

0 Likes
0
11
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-09-12 11:37 AM

Hi @Youssef-asec,

 

What is the difference between the summation and the value? is it consistent over time?

 

Aside from that difference, are other measurements expected—such as power, energy, etc.?

 

Also, what is the firmware version on these meters?

 

@rohith-s @Sidharthan do you have any additional comments on this?

 

Regards,
JD

Reply
Charles_Murison
Picard Charles_Murison Picard
Picard

Posted: ‎2025-09-12 02:33 PM

0 Likes
0
7
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-09-12 02:33 PM

Hello @Youssef-asec ,

What kind of tolerances doe your system have? What is the differences in readings. 

Let us say for example that the CTs are 1% accurate and meter is 0.1%, this means meter could be as much as 1.1% off and still be within rated accuracy. Now lets say that the 2 meters are 1.1% in one direction and the other meter is 1.1% in the opposite direction. this means the current could be different by 3.3% and still be within stated accuracy. 

The numbers are just an example and different CTs have different ratings and some will have ratings that differ depending on the current through the CT. The math is also the simplified example the math for tolerances gets a little more complex but a 3% plus difference is not unexpected.

There is also how are you collecting the data, latencies in communication, screen update rates and the often second by second variation of current makes trying to compare real time values very very difficult. A better test could be to have all meters be time sync'd, then integrate or average the current over a set period of time and compare the combined results.

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities
Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore