Important Announcement: WELCOME to the new Schneider Electric Community! Community is now no longer part of Exchange, and is now rebranded under se.com. If you have any bookmarks and links saved, we request you to update them to ensure that you continue accessing our community from this new location. For any issues that you might encounter as part of this change, please reach out to SchneiderCommunity.Support@se.com, and the team will help to get your issues resolved.
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
Send Invite Cancel
82523members
350129posts

Medidor ION8650C Reiniciando - IRIG-B

Metering & Power Quality

Collaborate with multiple experts and discuss various topics about Power Meters and Power Quality. From design & implementation to troubleshooting and more, get support from experts and share your experiences by subscribing to the Schneider Electric Exchange forum today.

Solved
lmgm-prolux
Ensign
Ensign
0 Likes
3
488

Medidor ION8650C Reiniciando - IRIG-B

Hola
Tenemos un problema con algunos medidores ION8650C. Cuando intentamos sincronizar los medidores a través de IRIG-B, comienzan a reiniciarse. Verificamos que la tensión de alimentación permanezca estable (125Vdc), por lo que no hay problema en el circuito de alimentación. Hicimos la prueba con otro GPS y sucede lo mismo. Al intentar sincronizar a través de RS-485, el medidor funciona perfectamente.
¿Has tenido este problema?

Attachments
Tags (3)

Accepted Solutions
Charles_Murison
Picard Picard
Picard

Re: Medidor ION8650C Reiniciando - IRIG-B

Hello,

 

What version of Firmware do you have? V4.31.1 had a number of updates to address irig-b. If not the latest version, can you update the meters?

https://www.schneider-electric.us/en/download/document/ION8650_V004.031.001/

L4 Prime for Advanced metering and Utilities

See Answer In Context

3 Replies 3
Charles_Murison
Picard Picard
Picard

Re: Medidor ION8650C Reiniciando - IRIG-B

Hello,

 

What version of Firmware do you have? V4.31.1 had a number of updates to address irig-b. If not the latest version, can you update the meters?

https://www.schneider-electric.us/en/download/document/ION8650_V004.031.001/

L4 Prime for Advanced metering and Utilities
lmgm-prolux
Ensign
Ensign
0 Likes
1
483

Re: Medidor ION8650C Reiniciando - IRIG-B

Estamos con firmware 4.30.0. Nuestro cliente hará la actualización de firmware mañana. Después de este procedimiento, respondo aquí si funcionó o no.

Muchas Gracias

 

lmgm-prolux
Ensign
Ensign
0 Likes
0
476

Re: Medidor ION8650C Reiniciando - IRIG-B

Hola charles!

Hicimos el procedimiento que usted indicó y funcionó. Los medidores comenzaron a sincronizarse a través de IRIG-B y dejaron de reiniciarse.
Muchas gracias.