Log Handles Descriptions - PM8000

Metering & Power Quality

Collaborate with multiple experts and discuss various topics about Power Meters and Power Quality. From design & implementation to troubleshooting and more, get support from experts and share your experiences by subscribing to the Schneider Electric Exchange forum today.

Solved
JoBeeLW
Crewman
Crewman
0 Likes
3
398

Log Handles Descriptions - PM8000

Hi,

 

I'm looking for the Log Handles Descriptions/Definitions on the PM8240 (PM8000) meter.

Need it to regulate a number of devices' log retrieval via log inserter.

 

Thank You.

Tags (2)

Accepted Solutions
Charles_Murison
Picard Picard
Picard
0 Likes
2
388

Re: Log Handles Descriptions - PM8000

Hello,

 

When using ION Setup, you can see the handle for setup and output registers by holding the ctrl and clicking on the tab.

Data recorder 1 is 0xF80,

Data recorder 10 is 0xF89

Data recorder 40 is 0xFB5

 

Please let me know if this does not help.

 

Charles

 

L4 Prime for Advanced metering and Utilities

See Answer In Context

3 Replies 3
Charles_Murison
Picard Picard
Picard
0 Likes
2
389

Re: Log Handles Descriptions - PM8000

Hello,

 

When using ION Setup, you can see the handle for setup and output registers by holding the ctrl and clicking on the tab.

Data recorder 1 is 0xF80,

Data recorder 10 is 0xF89

Data recorder 40 is 0xFB5

 

Please let me know if this does not help.

 

Charles

 

L4 Prime for Advanced metering and Utilities
Charles_Murison
Picard Picard
Picard
0 Likes
0
383

Re: Log Handles Descriptions - PM8000

If this has answered your question, please mark as solution.

 

Thank you,

Charles

 

L4 Prime for Advanced metering and Utilities
JoBeeLW
Crewman
Crewman
0 Likes
0
380

Re: Log Handles Descriptions - PM8000

Hi Charles,

 

Exactly what I needed.

 

Thank You!