Continue
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • My Subscriptions
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Is there any IEEE 519:2014 framework compatible with ION8650A available?

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • Is there any IEEE 519:2014 framework compatible with ION8650A available?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Charles_Murison Champion
582
Mehran_Mehrnia
Mehran_Mehrnia Champion
217
Ramasamy_N
Ramasamy_N Champion
117
View All

Recommended Forums

  • SmartConnector Forum

Related Products
product field
PowerLogic
PowerLogic ION8650 series

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Start a Topic
Solved
Sreejith_KM
Sreejith_KM Contributor
Contributor

Posted: ‎2023-02-01 11:49 AM

0 Likes
8
4637
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-02-01 11:49 AM

Is there any IEEE 519:2014 framework compatible with ION8650A available?

Hi

We have a requirement where we need to show IEEE 519:2014 compliance report using PME and ION8650A.

Understand it is not default available in the meter. Do we have any framework compatible with ION8650A available? Or can we use the framework for ION9K in ION8650A?

  • Thumbnail of PowerLogic ION8650 series
    PowerLogic
    PowerLogic ION8650 series
View products (1)
Labels
  • Labels:
  • ION Guidebooks
  • ION8000
  • Power Quality
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
N4th4n13L
N4th4n13L Troubleshooter
Troubleshooter

Posted: ‎2023-02-02 07:11 PM

2 Likes
1
4609
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-02-02 07:11 PM

Hello @Sreejith_KM ,

 

I created the attached framelet when working on this for the US template. I would only recommend pushing this with PME Designer as it will likely overwrite several modules in the existing framework. I know I had to remove most the EN50160 recorders for this to fit. I was using the US template so it also utilizes the floating nominal framework for nominal voltage. It also uses some overlapping modules with the 4-30 framework, and may create duplicate modules when pushing. I remember the label names need to be correct feeding the data recorders for the PME report to run as well. I used a 9000 meter to reference the label names to make sure they're correct. 

See Answer In Context

Attachments
8650A_IEEE519_V3.zip
Reply
Replies 8
N4th4n13L
N4th4n13L Troubleshooter
Troubleshooter

Posted: ‎2023-02-01 02:53 PM

2 Likes
7
4627
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-02-01 02:53 PM

Hello,

 

The US V4.2.0.2.2 template does include the framework in it. It's built based on the ION 9000 framework, but had to allocate modules a little differently based on core framework already in the US template.

Reply
Sreejith_KM
Sreejith_KM Contributor
Contributor

Posted: ‎2023-02-01 09:56 PM

0 Likes
4
4621
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-02-01 09:56 PM

Thanks for the reply.

So, guess for India with FW V4.40.1, we don't have any option than making a new custom framework.

Reply
Charles_Murison
Charles_Murison Champion
Champion

Posted: ‎2023-02-02 10:12 AM

1 Like
3
4615
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-02-02 10:12 AM

Hello @Sreejith_KM , have you talked with Pradip Maity? I believe there is currently a piolet running in India with ION8650 meters and US V4.2.0.2.2 template.


Regarding a custom framework, if you want to create your own you are welcome to do so, there is nothing saying you cannot. Note that the IEE519 is a complex framework with many modules and PME is very specific as to what needs to be recorded for the report to work.

Regards,

Charles

L4 Prime for Advanced metering and Utilities
Reply
N4th4n13L
N4th4n13L Troubleshooter
Troubleshooter

Posted: ‎2023-02-02 07:11 PM

2 Likes
1
4609
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-02-02 07:11 PM

Hello @Sreejith_KM ,

 

I created the attached framelet when working on this for the US template. I would only recommend pushing this with PME Designer as it will likely overwrite several modules in the existing framework. I know I had to remove most the EN50160 recorders for this to fit. I was using the US template so it also utilizes the floating nominal framework for nominal voltage. It also uses some overlapping modules with the 4-30 framework, and may create duplicate modules when pushing. I remember the label names need to be correct feeding the data recorders for the PME report to run as well. I used a 9000 meter to reference the label names to make sure they're correct. 

Attachments
8650A_IEEE519_V3.zip
Reply
Sreejith_KM
Sreejith_KM Contributor
Contributor

Posted: ‎2023-02-03 12:54 AM

0 Likes
0
4601
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-02-03 12:54 AM

Thanks very much @Charles_Murison for the response.

Lately came to know about this project and now connected with Pradip.

Reply
Sreejith_KM
Sreejith_KM Contributor
Contributor

Posted: ‎2023-02-03 01:01 AM

0 Likes
0
4600
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-02-03 01:01 AM

Thanks very much @N4th4n13L, appreciate your help in this regard.

Will update the shared info to backend team to adapt & see.

Reply
LarryP
LarryP
Explorer

Posted: ‎2024-11-21 11:35 AM

0 Likes
1
3231
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-11-21 11:35 AM

For the 8650A voltage range setting.  Is the below correct?; i.e. the radio buttons L-L while the nominal is L-N?

LarryP_0-1732217631802.png

 

Reply
Charles_Murison
Charles_Murison Champion
Champion

Posted: ‎2024-11-22 09:00 AM

0 Likes
0
3217
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-11-22 09:00 AM

Hello @LarryP ,

 

Will need to refer to the IEEE519 Standard to confirm if the voltage is VLL or VLN. As far as the meter is concerned, this setting will change an External Numeric register that has enumeration for PME reports. This setting will also affect the table ION Setup uses to program the harmonic limits. This does not affect the sag/swell module.

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities
Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore