Hi Comunity,
I have a small issue with Power total always 0, while the different Power By Phases are having reading,
Set made is
6000:5
kWa = 0.195 MW
kWb= 0.191 MW
kWc= 0.190 MW
kW tot = 0 MW
B.R.
Link copied. Please paste this link to share this article on your social media post.
Hi,
Issue was solved by changing the
UseFundkVar to ON
Scale Rev Param to ON
Many thanks,
Link copied. Please paste this link to share this article on your social media post.
Hello @EA23 ,
Have you tried to paste the default template on the meter again?
Regards,
Charles
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Hello @EA23 ,
Likely there are other External Boolean modules that are typically on be default and currently off. I would strongly recommend, if possible, to re-apply the meter's template to ensure that all default external Boolean modules are turned on that should be on.
Regards,
Charles