【HDPM6000】CT configuration when setting Delta
Metering & Power Quality
  • EcoStruxure Power & Grid
  • 【HDPM6000】CT configuration when setting Delta
Charles_Murison
Charles_Murison Champion
582
Mehran_Mehrnia
Mehran_Mehrnia Champion
217
Ramasamy_N
Ramasamy_N Champion
117
Miyai
Miyai
Contributor
Posted: ‎2024-11-20 04:43 PM
1328
If Supply type is set to Delta, is any special setting required to set the CT circuit configuration?
I cannot select the CT item even if I open the Channel Cfg tab.
For some reason, only channels 83 and 84 are selectable.
The head unit firmware version is 58.7.
If the supply type is set to "Wye" or "Split", the CT configuration can be set correctly.
This issue only occurs in the delta setting.
I need some advice on which parts I need to enable.
Miyai
  • HDPM6000
Mehran_Mehrnia
Champion
Posted: ‎2024-11-21 10:56 AM . Last Modified: ‎2024-11-21 11:19 AM
1
1308
Hi @Miyai
As mentioned in HDPM6000 Installation guide, there are two methods to assign channels to a circuit which are 'Automatic Grouping' and 'Manual Grouping' depending if the 'Manually assign channels to circuits' box in the lower right hand corner of the Channel Cfg page has been checked or not.
If you uncheck that box, which means Automatic Grouping, then you will have the option to define and create circuits by selecting 'Add to circuit' box between channels on the same breaker, and uncheck the 'Add to circuit' box between channels of different breakers.
Best Regards,
-Mehran
L3 Expert Advanced metering
Mehran_Mehrnia
Champion
1
1308
Hi @Miyai
Best Regards,
-Mehran
Miyai
Miyai
Contributor
Posted: ‎2024-11-25 07:07 PM
Hi @Mehran_Mehrnia
Thank you for your advice.
I was able to change the CT configuration by unchecking the box at the bottom right of the screen.
Miyai