Is 3 wire cable needed for 2 wire RS485 systems?

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • Is 3 wire cable needed for 2 wire RS485 systems?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Picard Charles_Murison Picard
478
Ramasamy_N
Captain Ramasamy_N Captain
113
Robert_Lee
Admiral Robert_Lee Admiral
92
Mehran_Mehrnia
Captain Mehran_Mehrnia Captain
89
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Metering & Power Quality
sesa71277_bridg
sesa71277_bridg Schneider Alumni (Retired)
Schneider Alumni (Retired)

Posted: ‎2014-08-27 06:42 PM

0 Likes
5
3329
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2014-08-27 06:42 PM

Is 3 wire cable needed for 2 wire RS485 systems?

 

When wiring for a 2 wire system using an EGX100, usually only a two pair and shielded cable is used.

As per the PM800 manual (Belden 9841) is recommended.

What should be done with the 0V terminal of the iEM3150 in this situation. 

Should 3 wire communication cable be used or should the shield terminal be connected to the 0V terminal?

Reply
  • All forum topics
  • Previous Topic
  • Next Topic
Replies 5
VictorMarincus
Sisko VictorMarincus Sisko
Sisko

Posted: ‎2014-08-28 01:21 AM

9 Likes
4
3075
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2014-08-28 01:21 AM

The GND or COMM or COMMON or '0V' (different notations on different devices) is used to obtain a balanced data transmission line. The function of the GND connection is to tie the signal grounds of all nodes on a network to one common ground potential. This is the only wiring rule for this connector - to connect the reference pin (of each RS485 driver) to the same reference. This ensures that the common mode voltage cannot exceed the specified value (see spec. for a RS-485 transceiver – voltage levels). If the devices have the ground connector (0V) this should be connected to each common connector of the other devices. This (loop) shall be earthed at one point only assuring that all notes have reference to the same potential (0V).

The shield (cable’s shield – notation SH, SHLD or symbol for Shielded Multiconductor Cable – see this) is used - tied at one point to earth ground - to shunt coupled noise and avoid creating ground loops. The SH or SHLD is present in all our devices. The documentation states whether the SH is connected to chassis or not (take the example of the ION7650). The chassis, further, shall be connected to a good earth ground – one end only.

So, getting back to your question:

1. when you have devices like PM800 you'll use a 2wire+shield cable

2. when you have devices like iEM3150/PM5000, etc you'll use a 3wire+shield cable

And here you can find a good FAQ on this topic: 3 Wire RS485 Vs. 2 Wire RS485.  | Chipkin Automation Systems

Regards,

Victor

Reply
JamesAZZO
Sisko | EcoXpert Master JamesAZZO Sisko | EcoXpert Master
Sisko | EcoXpert Master

Posted: ‎2014-08-28 06:58 AM

0 Likes
0
3075
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2014-08-28 06:58 AM

Great explanation Victor.

Reply
sesa71277_bridg
sesa71277_bridg Schneider Alumni (Retired)
Schneider Alumni (Retired)

Posted: ‎2014-08-28 03:30 PM

0 Likes
1
3075
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2014-08-28 03:30 PM

Thanks for the great answer. Therefore from your response, I am assuming if I have a two wire system, it is Ok to connect the 0V terminal to the Shield terminal in the meters and tie to the earth ground at one point?

Reply
VictorMarincus
Sisko VictorMarincus Sisko
Sisko

Posted: ‎2014-08-29 01:41 AM

1 Like
0
3075
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2014-08-29 01:41 AM

Yes that is correct. Here is the schema presented on the PM5000 installation guide on which I highlighted the ground connections. Hope this is clear now.

4435

Reply
michael_franz
Admiral michael_franz
Admiral

Posted: ‎2017-06-30 11:34 AM

0 Likes
0
3075
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2017-06-30 11:34 AM

Victor:

Great write up.  Some RS485 systems get by with two wires but with metering I like the shield.

Michael

Reply
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of