Hi
I'm having a hard time trying to figure out which modbus variable I should request.
I need to get the phasor's angle for every current and voltage. I can't find the va,vb,vc,ia,ib and ic angles.
I can't find it in the modbus table, any hint or suggestion will be fully appreciated.
I used the official modbus document named:
ION9000_Modbus_Map_002.000.000.xlsx
I'm using the web server to get this image but non of the modbus requested values gives me the angle values in the image.
Link copied. Please paste this link to share this article on your social media post.
Hi @peperoca116
In order to read the Voltage and Current magnitudes and angles, read registers such as:
Voltage X, H1 Angle
Voltage X, H1 Magnitude
Current X, H1 Angle.
Current X, H1 Magnitude
For example:
Current A, H1 Magnitude, with Modbus register: 24430
Current A, H1 Angle with Modbus register: 24432
Best Regards,
-Mehran
L3 Expert Advanced metering
Link copied. Please paste this link to share this article on your social media post.
Hi @peperoca116
In order to read the Voltage and Current magnitudes and angles, read registers such as:
Voltage X, H1 Angle
Voltage X, H1 Magnitude
Current X, H1 Angle.
Current X, H1 Magnitude
For example:
Current A, H1 Magnitude, with Modbus register: 24430
Current A, H1 Angle with Modbus register: 24432
Best Regards,
-Mehran
L3 Expert Advanced metering
Link copied. Please paste this link to share this article on your social media post.
That was exactly what I needed!
Thanks 🙂