Continue
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • My Subscriptions
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

ION9000 - Pre-triggered and Post-triggered Waveform Recording

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • ION9000 - Pre-triggered and Post-triggered Waveform Recording
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Charles_Murison Champion
582
Mehran_Mehrnia
Mehran_Mehrnia Champion
216
Ramasamy_N
Ramasamy_N Champion
117
View All

Recommended Forums

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Start a Topic
Solved
jonathanzamban
jonathanzamban
Explorer

Posted: ‎2020-06-23 02:47 AM

0 Likes
8
5407
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-06-23 02:47 AM

ION9000 - Pre-triggered and Post-triggered Waveform Recording

I am trying to change the waveform recording period pre and post power quality events on the ION9000 meter. However, I have come across the following limits: 30 seconds pre-event and 10 seconds post-event.

 

I am looking to set the limits as 5 seconds pre-event and 55 seconds post-event.

Does anyone know if that is possible on the ION9000?

 

Thanks in advance.

Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Charles_Murison
Charles_Murison Champion
Champion

Posted: ‎2020-06-25 08:53 AM

2 Likes
3
5382
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-06-25 08:53 AM

Hello @jonathanzamban ,

 

The 30 second maximum is the limit within the ION Setup wizard this is not the same as the device limit, if you set the meter into advanced configuration you can change the pre and post values to be higher. You are limited more by the shared buffer memory (different than long term memory of 10BM for each data recorder/waveform recorder)

 

For the ION9000, assume that each waveform is ~10kb (a bit lower than this but 10 makes math easier) if you are using 32x54 and have 50Hz system and want to record 61 seconds, 5 seconds before(5 waveforms), the event (1 waveform), and 55 seconds after (51 waveforms). So you will be using ~600 kb (again rounding up) of buffer memory per waveform recorder (default is 6). You could use more if your buffer depth is larger.

 

Please note that in your screenshot, this is configuring the "Burst data" (data recorder) which is different from the waveform recording (waveform recorder). When you set the meter to advanced configuration you can see the following setup registers. This is where you can change the pre post trigger values. Be sure to apply this to all waveform recorders with the same trigger (sag/swell vs transient)

 

 

L4 Prime for Advanced metering and Utilities

See Answer In Context

Tags (1)
  • Tags:
  • english
Reply
Charles_Murison
Charles_Murison Champion
Champion

Posted: ‎2020-07-03 08:57 AM

1 Like
0
5362
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-07-03 08:57 AM

Hello @jonathanzamban ,

 

COMTRADE modules are a separate set of modules that have their own setup registers including how many waveforms to save before overwriting. In the advanced mode you can access these modules and update the setup registers. 1 module is for sag/swell waveform captures, the other is for transient waveform captures. I can't remember off the top of my head which one is which.

 

For the buffer depth the wizard may have some limits, however if you can access the the modules with advanced configuration you are likely to change this value. Please note that buffer memory is not an endless resource on the meter and shared with a number of other modules. ION reference does have some information on what the values in buffer setup register can be.

 

Charles

L4 Prime for Advanced metering and Utilities

See Answer In Context

Tags (1)
  • Tags:
  • english
Reply
Replies 8
Charles_Murison
Charles_Murison Champion
Champion

Posted: ‎2020-06-23 02:42 PM

2 Likes
7
5394
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-06-23 02:42 PM

Hello @jonathanzamban 

 

Have you looked at the ION Reference (7EN02-0290-11) page 501 "Pre-trigger Records and Post-trigger Records: detailed operation" One item to consider is the waveform capture format (samples per cycle x # cycles) 32x54 requires less waveforms together to reach 61 seconds than  64x14.

 

You may need to program the meter using advance configuration to use the Pre-trigger and Post trigger settings.

 

Charles

L4 Prime for Advanced metering and Utilities
Tags (1)
  • Tags:
  • english
Reply
jonathanzamban
jonathanzamban
Explorer

Posted: ‎2020-06-25 04:12 AM

0 Likes
6
5389
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-06-25 04:12 AM

Hi @Charles_Murison

 

Thanks for the explanation.

 

I understand that by reducing the samples per cycle, I will be able to record more cycles within one waveform record. However, what is still not clear to me is what would be the maximum record length (in seconds) that I can have for one event. On ION Setup I have the option to set:

 

Pre-trigger recording: Up to 30 seconds

Post-trigger recording: Up to 10 seconds

 

ION_Setup.PNG

 

As far as I have understood, this is the limit for a single event. Am I correct?

Then, my question would be how does these limits (pre/post-trigger) are related with the waveform capture format that I would choose. For example, if I would change from 32x54 to 16x96 (54 cycles * 0.02 sec = 1.08 sec, whereas 96 cycles * 0.02 sec = 1.92 sec), would that affect my waveform recording length (sec)?

 

I am not sure if I have clarified more my question or made it even more confusing, but I would really appreciate if you could please help me with it.

 

Thank you,

Jonathan.

Tags (1)
  • Tags:
  • english
Reply
Charles_Murison
Charles_Murison Champion
Champion

Posted: ‎2020-06-25 08:53 AM

2 Likes
3
5382
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-06-25 08:53 AM

Hello @jonathanzamban ,

 

The 30 second maximum is the limit within the ION Setup wizard this is not the same as the device limit, if you set the meter into advanced configuration you can change the pre and post values to be higher. You are limited more by the shared buffer memory (different than long term memory of 10BM for each data recorder/waveform recorder)

 

For the ION9000, assume that each waveform is ~10kb (a bit lower than this but 10 makes math easier) if you are using 32x54 and have 50Hz system and want to record 61 seconds, 5 seconds before(5 waveforms), the event (1 waveform), and 55 seconds after (51 waveforms). So you will be using ~600 kb (again rounding up) of buffer memory per waveform recorder (default is 6). You could use more if your buffer depth is larger.

 

Please note that in your screenshot, this is configuring the "Burst data" (data recorder) which is different from the waveform recording (waveform recorder). When you set the meter to advanced configuration you can see the following setup registers. This is where you can change the pre post trigger values. Be sure to apply this to all waveform recorders with the same trigger (sag/swell vs transient)

 

 

L4 Prime for Advanced metering and Utilities
Tags (1)
  • Tags:
  • english
Reply
jonathanzamban
jonathanzamban
Explorer

Posted: ‎2020-07-03 08:39 AM

0 Likes
2
5364
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-07-03 08:39 AM

Hi @Charles_Murison,

 

Thanks for your reply, it was very useful.

 

I changed the Pre/Post-triggered settings via meter advanced configurations and was able to see the waveforms recorded using the Power Monitoring Expert (PME 2020) as expected.

 

However, when I retrieved the COMTRADE files from the ION9000 FTP server, they did not contain more than two/three seconds of waveforms altogether.

 

Also, I could not set the Buffer Depth to a value larger than 60 sec, because the wizard did not allow me to set different values for the different modules (V1/2/3 Sag/Swell/Transient & I1/2/3 Sag/Swell/Transient).

 

Would you know in which parameter is the limitation that does not put all the waveforms recorded into the COMTRADE files?

 

Thank you very much for your help so far,

Jonathan.

Tags (1)
  • Tags:
  • english
Reply
Charles_Murison
Charles_Murison Champion
Champion

Posted: ‎2020-07-03 08:57 AM

1 Like
0
5362
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-07-03 08:57 AM

Hello @jonathanzamban ,

 

COMTRADE modules are a separate set of modules that have their own setup registers including how many waveforms to save before overwriting. In the advanced mode you can access these modules and update the setup registers. 1 module is for sag/swell waveform captures, the other is for transient waveform captures. I can't remember off the top of my head which one is which.

 

For the buffer depth the wizard may have some limits, however if you can access the the modules with advanced configuration you are likely to change this value. Please note that buffer memory is not an endless resource on the meter and shared with a number of other modules. ION reference does have some information on what the values in buffer setup register can be.

 

Charles

L4 Prime for Advanced metering and Utilities
Tags (1)
  • Tags:
  • english
Reply
Robert_Lee
Robert_Lee Champion
Champion

Posted: ‎2020-09-01 05:15 PM

1 Like
0
5351
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-09-01 05:15 PM

The Buffer Depth is taking memory from a pool of 10 Mb Total (spread out over all DRE/DSR/WFR/WHR modules).  This is fast memory to allow fast caching and then those records are transferred periodically to slower (larger) memory.

The ION Setup wizard was designed to allow for most common uses where most users want pre-data (as this was historically harder to obtain as this is prior to the triggering event).  The wizard is designed to compute the # of records for Pre/Post and show that in a user-friendly manner expressed as seconds (instead of having to figure things out based on nominal frequency and sampling size).

In some instances the memory restriction based on what you want to do will require that you will need to heavily restrict all other meter functions (and waiting for 60 seconds of waveforms being triggered and then being uploaded is very time intensive).

As for the COMTRADE restriction, this will also be problematic as this means that in order for the firmware to generate 60 seconds of individual files (1 file = 1 record) so this will likely be hundreds of files (and likely there is an upper limit for the COMTRADE module).

Tags (1)
  • Tags:
  • english
Reply
Robert_Lee
Robert_Lee Champion
Champion

Posted: ‎2020-09-01 05:26 PM . Last Modified: ‎2020-09-01 05:26 PM

1 Like
1
5350
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-09-01 05:26 PM

Also the 30 seconds/10 seconds is Data Burst logging which is NOT waveforms but essentially data logging of parameters (think 1/2 cycle RMS which is logging approx every 8 ms).

Waveforms can operate in the same manner but there is no wizard to allow the adjustment of the Pre/Post buffer settings (the wizard will however not adjust those settings if they are configured in Advanced mode).  We felt that very few users will be wanting that type of functionality and those that did would be very advanced ION users who would be comfortable in doing adjustments in Advanced programming (and not depend on a wizard to account for every situation).

Tags (1)
  • Tags:
  • english
Reply
Charles_Murison
Charles_Murison Champion
Champion

Posted: ‎2020-09-02 08:09 AM

1 Like
0
5344
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-09-02 08:09 AM

One item to note, I believe when using the pre-trigger and post trigger settings, the Commtrade modules will only save 1 waveform, and not all of the back to back waveforms.

L4 Prime for Advanced metering and Utilities
Tags (1)
  • Tags:
  • english
Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore