ION9000 Modbus Issue

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • ION9000 Modbus Issue
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Picard Charles_Murison Picard
492
Ramasamy_N
Captain Ramasamy_N Captain
115
Mehran_Mehrnia
Captain Mehran_Mehrnia Captain
93
Robert_Lee
Admiral Robert_Lee Admiral
92
View All
Related Products
product field
Schneider Electric
PowerLogic ION9000

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Metering & Power Quality
sbogavilli
Crewman sbogavilli
Crewman

Posted: ‎2025-06-26 11:44 PM

0 Likes
1
99
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-06-26 11:44 PM

ION9000 Modbus Issue

Hello everyone,

 

Checking if some experts had faced a similar issue?

Modbus Map used is version_004.005.000 (attached)

1) We are commissioning one of our sites with an ION 9000 meters and want to retrieve values via the Modbus interface.

 

We set the frequency to 25 Hz by simulating the input to the ION but the frequency in our GeoSCADA via Modbus is showing as 25.06 Hz (32-bit Floating Point)

 

sbogavilli_0-1751005990557.png

 

sbogavilli_1-1751005990576.png

 

 

We investigated the 2x 16 bit register values which are being sent across Modbus to represent 25 Hz, they are shown above as 16840 & 32768, these in Hex are 41C8 (=16840 Decimal) & 8000 (=32768 Decimal)

 

When we put the 32 bits combined 41C88000 into a calculator it does compute to 25.0625 Hz

 

We have checked this with two separate calculators

 

Floating Point to Hex Converter

 

IEEE-754 Floating Point Converter

 

sbogavilli_2-1751005990578.png

 

 

We believe the value sent across to represent 25 Hz should be 41C80000

 

sbogavilli_3-1751005990580.png

 

 

We only noticed this discrepancy on Frequency as it was stable at a value of 25, the difference albeit small is significant when measuring frequency.

 

The error is present on both addresses returning frequency

 

sbogavilli_4-1751005990581.png

 

 

We also saw slight differences in current, voltage etc when we simulated those too so they potentially have a similar error.

 

2) There also appears to be a two register offset compared to what is quoted in the Modbus map, to address register 3110 I had to request register 3108.

  • Thumbnail of PowerLogic ION9000
    Schneider Electric
    PowerLogic ION9000
View products (1)
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic
Reply 1
Mehran_Mehrnia
Captain Mehran_Mehrnia Captain
Captain

Posted: ‎2025-06-27 06:51 AM

0 Likes
0
85
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-06-27 06:51 AM

Hi @sbogavilli 

 

1- As mentioned in the ION9000 user guide, Electrical Characteristics, the frequency accuracy class according to IEC 61557-12 is Class 0.02, which means ±10 millihertz. In a 50 Hz system, this corresponds to an acceptable range of 49.99 Hz to 50.01 Hz.

Mehran_Mehrnia_0-1751029882784.png

However, as stated in the voltage table, the specified frequency accuracy will be maintained when the injected voltage frequency is within 50/60 Hz ±15%. This means that for a 50 Hz system, the claimed accuracy is valid when the frequency is between 42.5 Hz and 57.5 Hz.

Mehran_Mehrnia_1-1751029992281.png

 

The meter can still measure parameters when the frequency is outside the specified range, but the claimed accuracy is not guaranteed.

 

2- This is dependent on how the Modbus client interprets register addressing.

Zero-based addressing (starts at 0)
One-based addressing (starts at 1)

So:

A client using one-based addressing will read 3110 & 3111
A client using zero-based addressing will read 3109 & 3110

 

Based on the ION9000 Modbus map, register 3108 is not associated with any valid data, unless there is a custom configuration in the meter's Modbus map.

 

Best Regards,

-Mehran

L3 Expert Advanced metering

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of