Hi @pucci
Theses are the statistical values derived from the current measurements on Phase A over a defined period.
Current A High: This is the maximum current recorded on Phase A during the measurement interval. It represents the peak value observed.
Current A Mean: This is the average current on Phase A over the measurement interval. It gives a general idea of the typical load on that phase.
Current A Low: This is the minimum current recorded on Phase A during the same interval. It shows the lowest point the current dropped to.
Best Regards,
-Mehran
L3 Expert Advanced metering
Link copied. Please paste this link to share this article on your social media post.
Hi @pucci
Theses are the statistical values derived from the current measurements on Phase A over a defined period.
Current A High: This is the maximum current recorded on Phase A during the measurement interval. It represents the peak value observed.
Current A Mean: This is the average current on Phase A over the measurement interval. It gives a general idea of the typical load on that phase.
Current A Low: This is the minimum current recorded on Phase A during the same interval. It shows the lowest point the current dropped to.
Best Regards,
-Mehran
L3 Expert Advanced metering