ION9000 Alarm Event Priority
Metering & Power Quality
Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.
Search in
Improve your search experience:
Exact phrase→Use quotes " "(e.g., "error 404")
Wildcard→Use * for partial words(e.g., build*, *tion)
AND / OR→Combine keywords(e.g., login AND error, login OR sign‑in)
Keep it short→Use 2–3 relevant words, not full sentences
Filters→Narrow results by section(Knowledge Base, Users, Products)
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Behavior such as waveform capture and logging are not affected by event priority.
The event priority is used to assign a value to the meter's event log and the front panel alarm indicator behavior. Where the priority will affect the meter's event log is if the priority is below the cutoff threshold example Priority=0, the meter will not write events to the meter's onboard event log. The alarm indicator may not indicate an alarm if priority is set to Info Only.
If you have software applications such as Power Monitoring Expert the event priority can determine some software behavior.
Behavior such as waveform capture and logging are not affected by event priority.
The event priority is used to assign a value to the meter's event log and the front panel alarm indicator behavior. Where the priority will affect the meter's event log is if the priority is below the cutoff threshold example Priority=0, the meter will not write events to the meter's onboard event log. The alarm indicator may not indicate an alarm if priority is set to Info Only.
If you have software applications such as Power Monitoring Expert the event priority can determine some software behavior.