ION9000 2CT wiring and configuration

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • ION9000 2CT wiring and configuration
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Picard Charles_Murison Picard
477
Ramasamy_N
Captain Ramasamy_N Captain
113
Robert_Lee
Admiral Robert_Lee Admiral
92
Mehran_Mehrnia
Captain Mehran_Mehrnia Captain
85
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Solved
joel_mora_soati
Lt. Commander joel_mora_soati
Lt. Commander

Posted: ‎2024-09-04 03:58 PM

0 Likes
4
908
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-09-04 03:58 PM

ION9000 2CT wiring and configuration

Hello Experts,

 

I have an ION9000 wired as 4W-WYE system with 3 CTs. I had an issue with the L2 current and my customer is asking me to change the ION configuration to work with 2CT.

 

I have done this configuration with low cost meters as PM5000 not in an ION9000. If I look at the basic parameters I don't see the option to select just 2CT.

Can you help me to understand the requierents of wiring and configuration?

 

Thanks. 

Attachments
Labels
  • Labels:
  • ION9000
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
DanL
Captain DanL Captain
Captain

Posted: ‎2024-09-06 08:19 AM

2 Likes
0
799
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-09-06 08:19 AM

correct, there is no additional configuration in meter parameters because the meter still sees three currents. The I2 secondary signal is the wired inverted summation of I1 and I3 (aka. residual current).

In a 4-WYE system, if there really is a 4th wire (ie. neutral) connected to the loads then using only 2 CTs may not result in accurate readings. See Blondel's theorem for more information:

https://en.wikipedia.org/wiki/Blondel%27s_theorem

 

See Answer In Context

Reply
Replies 4
Charles_Murison
Picard Charles_Murison Picard
Picard

Posted: ‎2024-09-04 04:43 PM

1 Like
3
897
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-09-04 04:43 PM

Hello @joel_mora_soati ,

 

If you look at the image you shared, you can see that the 2 CT method using the I1 and I3 feed into I2 "backwards". What this does on a physical level is give -(I1+I3) signal into the input of I2. The result is in system with only 3 current paths (I1,I2,I3), I2 would be the equivalent to what a CT would give. When you have 4 current paths (I1+I2+I3+N) you cannot use this method. You need 1 less CT than path minimum for accurate readings.

 

Regards,

Charles

 

L4 Prime for Advanced metering and Utilities
Reply
joel_mora_soati
Lt. Commander joel_mora_soati
Lt. Commander

Posted: ‎2024-09-04 05:06 PM

0 Likes
2
896
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-09-04 05:06 PM

Thanks @Charles_Murison.

Just to confirm there is no aditional configuration in meter parameters?

Reply
Charles_Murison
Picard Charles_Murison Picard
Picard

Posted: ‎2024-09-05 01:36 PM

1 Like
0
832
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-09-05 01:36 PM

Hello @joel_mora_soati ,

 

I want to mention again that the 2 CT method is intended for Delta systems where there are only 3 current conductors. If you use the 2 CT method as shown in the diagram, the meter will not be able to detect any neutral current. 

The meter's Volts mode will be the only configuration that would change based on how the meter is wired.

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities
Reply
DanL
Captain DanL Captain
Captain

Posted: ‎2024-09-06 08:19 AM

2 Likes
0
800
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-09-06 08:19 AM

correct, there is no additional configuration in meter parameters because the meter still sees three currents. The I2 secondary signal is the wired inverted summation of I1 and I3 (aka. residual current).

In a 4-WYE system, if there really is a 4th wire (ie. neutral) connected to the loads then using only 2 CTs may not result in accurate readings. See Blondel's theorem for more information:

https://en.wikipedia.org/wiki/Blondel%27s_theorem

 

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of