Continue
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • My Subscriptions
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

ION8800B ftp not allow to paste CID file

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • ION8800B ftp not allow to paste CID file
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Charles_Murison Champion
582
Mehran_Mehrnia
Mehran_Mehrnia Champion
216
Ramasamy_N
Ramasamy_N Champion
117
View All

Recommended Forums

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Start a Topic
Solved
Yut
Yut
Leader

Posted: ‎2019-11-27 01:30 AM

0 Likes
12
3339
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-11-27 01:30 AM

ION8800B ftp not allow to paste CID file

I open the ftp:// but cannot paste CID file nor from CET850.

The firmware is V370 replaced by  V370_8800B_61850.upg I used the V362e templates because I could not find the V370e template. Any suggestion. I did 61850 with other meter before with ION8800 V362 it was OK.

 

 

 
 
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Charles_Murison
Charles_Murison Champion
Champion

Posted: ‎2019-11-28 09:34 AM

0 Likes
8
3329
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-11-28 09:34 AM

Hello Yut,

 

Personally I find using Windows Explorer rather than Internet explorer easier to work with for FTP. The address bar would be the same: ftp://[ipaddress]

L4 Prime for Advanced metering and Utilities

See Answer In Context

Reply
Charles_Murison
Charles_Murison Champion
Champion

Posted: ‎2019-12-02 10:09 AM

0 Likes
2
3315
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-12-02 10:09 AM

Hello Yut,

 

I would not recommend making changes to the IEC 61850 MMTR, MMXU etc as this could lead to confusion if someone assumes the meter is still in default configuration. Does the 8800 ICD file have GGIO Cust AI? This is where I would put the custom measurements. You are limited to 16 measurements.

L4 Prime for Advanced metering and Utilities

See Answer In Context

Reply
Replies 12
Charles_Murison
Charles_Murison Champion
Champion

Posted: ‎2019-11-27 04:47 PM

0 Likes
11
3337
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-11-27 04:47 PM

Are you using addition 1 or 2? Can you attach your CID file?

L4 Prime for Advanced metering and Utilities
Reply
Yut
Yut
Leader

Posted: ‎2019-11-27 07:49 PM

0 Likes
0
3335
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-11-27 07:49 PM

I redo from beginning using Edition 2 with the SE_ION_8800-B-Onb5-F01_E2V01.ICD.

Please see the CID file  Is there any security restriction on new ION8800 V370 ? 

 

 

Reply
Yut
Yut
Leader

Posted: ‎2019-11-27 08:12 PM

0 Likes
9
3331
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-11-27 08:12 PM

I can open FTP but cannot paste anything.

ION8800 FTP.jpg

Reply
Charles_Murison
Charles_Murison Champion
Champion

Posted: ‎2019-11-28 09:34 AM

0 Likes
8
3329
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-11-28 09:34 AM

Hello Yut,

 

Personally I find using Windows Explorer rather than Internet explorer easier to work with for FTP. The address bar would be the same: ftp://[ipaddress]

L4 Prime for Advanced metering and Utilities
Reply
Yut
Yut
Leader

Posted: ‎2019-11-28 04:54 PM

0 Likes
0
3327
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-11-28 04:54 PM

I try the Windows Explore too.

Wonder I used to do it before with the old firmware version.

Reply
Yut
Yut
Leader

Posted: ‎2019-11-28 08:44 PM

0 Likes
6
3325
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-11-28 08:44 PM

I change the computer then install CET850 V3.1.2 everything is OK.

New computer is Windows 10 Pro the  old one using Windows 7 .

The error message showed 

This site can’t be reached

The webpage at ftp://0:0@192.168.2.11/ might be temporarily down or it may have moved permanently to a new web address.

ERR_FTP_COMMAND_NOT_SUPPORTED
 
When use Windows Explorer it runs OK with new computer.
 
Thank you Charles
Reply
Yut
Yut
Leader

Posted: ‎2019-11-29 01:04 AM

0 Likes
5
3323
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-11-29 01:04 AM

Finally I got it work when test with TriangleMircro tools. Next how to customize the measurement aside from factory default any advice please.

ION8800IEC61850Test.jpg

Reply
Charles_Murison
Charles_Murison Champion
Champion

Posted: ‎2019-11-29 10:00 AM

0 Likes
4
3321
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-11-29 10:00 AM

Hello,

 

Not sure what customization you want to make.

L4 Prime for Advanced metering and Utilities
Reply
Yut
Yut
Leader

Posted: ‎2019-12-01 11:34 PM

0 Likes
3
3318
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-12-01 11:34 PM

For example we want to add value from store module that store end of month energy reading or daily kWh reading.

How about the IEC61850 modules each were set after the CID file has been loaded. If I edit the link will it be changed in

the CID file ?

 

IEC61850MMTR1.jpg 

Reply
Charles_Murison
Charles_Murison Champion
Champion

Posted: ‎2019-12-02 10:09 AM

0 Likes
2
3315
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-12-02 10:09 AM

Hello Yut,

 

I would not recommend making changes to the IEC 61850 MMTR, MMXU etc as this could lead to confusion if someone assumes the meter is still in default configuration. Does the 8800 ICD file have GGIO Cust AI? This is where I would put the custom measurements. You are limited to 16 measurements.

L4 Prime for Advanced metering and Utilities
Reply
Yut
Yut
Leader

Posted: ‎2019-12-02 07:45 PM

0 Likes
0
3310
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-12-02 07:45 PM

That is great I will work on AI.

This is the first project of the Utility here in Thailand about IEC61850 our ION8800 was chosen to be the model for IEC61850 Learning Center I'd like to give them the best.

Reply
Yut
Yut
Leader

Posted: ‎2019-12-02 08:17 PM

0 Likes
0
3307
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-12-02 08:17 PM

I work with GGIO Cust AI try to add kWh del and kvarh del int  to Anln1 and Anln2 they work fine.

Thank you very much.

 

IEC61850CUSTAI.jpg

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore