Hello,
I'm looking for the modbus registers with the statuses of the digital / relay outputs of a PM5000 meter.
In all available register lists I found a lot of statusus around the digital outputs (e.g. operating mode, control mode...), but not the simple actual status of the output (ON/OFF or ENERGIZED/DE-ENERGIZED).
Do I have an misstake?On which register can I found these statusus?
Thanks a lot and best regards
Sven
Link copied. Please paste this link to share this article on your social media post.
Hello Seven,
You can read the Modbus register 2403 (UINT16) to check the current status of Digital outputs (DO1,DO2) and Relays (DO3,DO4) in BITMAP format.
For example: The read value will be 15 (Binary: 1111) when all the 4 outputs are ON.
Regards,
Ramasamy N
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Hello Ramasamy,
thank you very much for your fast response.
Best regards
Sven