PM5000 Modbusregister for Output Status

Metering & Power Quality

Collaborate with multiple experts and discuss various topics about Power Meters and Power Quality. From design & implementation to troubleshooting and more, get support from experts and share your experiences by subscribing to the Schneider Electric Exchange forum today.

Solved
Sven_Kermer
Lieutenant JG Lieutenant JG
Lieutenant JG
0 Likes
2
356

PM5000 Modbusregister for Output Status

Hello,

 

I'm looking for the modbus registers with the statuses of the digital / relay outputs of a PM5000 meter.

In all available register lists I found a lot of statusus around the digital outputs (e.g. operating mode, control mode...), but not the simple actual status of the output (ON/OFF or ENERGIZED/DE-ENERGIZED).

Do I have an misstake?On which register can I found these statusus?

 

Thanks a lot and best regards

Sven


Accepted Solutions
Ramasamy_N
Commander Commander
Commander

Re: PM5000 Modbusregister for Output Status

Hello Seven, 

 

You can read the Modbus register 2403 (UINT16) to check the current status of Digital outputs (DO1,DO2) and Relays (DO3,DO4) in BITMAP format.

 

For example: The read value will be 15 (Binary: 1111) when all the 4 outputs are ON. 

 

Regards, 

Ramasamy N

See Answer In Context

2 Replies 2
Ramasamy_N
Commander Commander
Commander

Re: PM5000 Modbusregister for Output Status

Hello Seven, 

 

You can read the Modbus register 2403 (UINT16) to check the current status of Digital outputs (DO1,DO2) and Relays (DO3,DO4) in BITMAP format.

 

For example: The read value will be 15 (Binary: 1111) when all the 4 outputs are ON. 

 

Regards, 

Ramasamy N

Sven_Kermer
Lieutenant JG Lieutenant JG
Lieutenant JG
0 Likes
0
345

Re: PM5000 Modbusregister for Output Status

Hello Ramasamy,

 

thank you very much for your fast response.

 

Best regards

Sven