Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

How is the frequency measured in PM8000?

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • How is the frequency measured in PM8000?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Charles_Murison Champion
566
Mehran_Mehrnia
Mehran_Mehrnia Champion
194
Ramasamy_N
Ramasamy_N Champion
115
View All

Recommended Forums

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Start a Topic
Solved
sesa74337_bridg
sesa74337_bridg Troubleshooter
Troubleshooter

Posted: ‎2019-11-26 03:50 PM

0 Likes
3
2313
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-11-26 03:50 PM

How is the frequency measured in PM8000?

Hi, All

 

We have a data centre customer trying to understand why the PM8000 showing 50.01 Hz frequency on the generator board when there was only the control power to the meter, no 3-phase voltage and current inputs.

 

How does the PM8000 measures the frequency?

 

Thanks

 

James R

Tags (1)
  • Tags:
  • PM8000 Frequency measurement
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
DanL
DanL Champion
Champion

Posted: ‎2019-11-28 12:13 PM

0 Likes
0
2299
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-11-28 12:13 PM

On the PM8000, the hardware is designed to allow measurement (of both voltage and frequency) between any pair of voltage terminals.

For frequency measurement, the meter prioritizes pairs of voltage terminals with high signal levels (V1-VN, V2-VN, V3-VN, V1-V2, V2-V3, V3-V1).

The PQA module has an output indicating which frequency channel is in use "PQA1 Power Frequency Channel".

On the PM8000, the channels are:

V1N = 8,
V2N = 9,
V3N = 10,
V12 = 12,
V23 = 13,
V31 = 14,

 

If a signal is not detected on any pair, then the meter will revert to a single ended measurement on one terminal with respect to the meter's floating internal ground. Usually the meter's internal circuits have the same frequency as the auxillary supply voltage.

In the customer's situation where the V1, V2, V3 terminals are disconnected, most likely there is detectable voltage frequency between the Neutral connection on the VN measurement terminal and the meter's internal circuits. Of course when all measurement terminals are disconnected at the meter, there will be no measured frequency.

See Answer In Context

Reply
Replies 3
Charles_Murison
Charles_Murison Champion
Champion

Posted: ‎2019-11-26 04:36 PM

0 Likes
2
2310
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-11-26 04:36 PM

Hello James,

 

This  is a very abridged version and there are much more fine details but the general summary is:

Meter will measure the period for the zero crossing on Phase A voltage. Inverse of period is frequency.

 

For you meter, if you do a manual waveform capture, is there any Voltage on Phase A? 

L4 Prime for Advanced metering and Utilities
Reply
Hal_Etheridge
Hal_Etheridge Champion
Champion

Posted: ‎2019-11-26 05:46 PM

0 Likes
1
2308
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-11-26 05:46 PM

Some ION meters have the hardware capability to measure frequency on one of phase A, B or C.  In that case if phase A is missing/below the allowed threshold then it would switch to phase B and then switch phase C if needed.  If none of the phases have a usable voltage waveform then my guess is that most likely the frequency register would go N/A.  There should be some mention in the meter documentation what exactly the behavior is for these situations though.

Reply
DanL
DanL Champion
Champion

Posted: ‎2019-11-28 12:13 PM

0 Likes
0
2300
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-11-28 12:13 PM

On the PM8000, the hardware is designed to allow measurement (of both voltage and frequency) between any pair of voltage terminals.

For frequency measurement, the meter prioritizes pairs of voltage terminals with high signal levels (V1-VN, V2-VN, V3-VN, V1-V2, V2-V3, V3-V1).

The PQA module has an output indicating which frequency channel is in use "PQA1 Power Frequency Channel".

On the PM8000, the channels are:

V1N = 8,
V2N = 9,
V3N = 10,
V12 = 12,
V23 = 13,
V31 = 14,

 

If a signal is not detected on any pair, then the meter will revert to a single ended measurement on one terminal with respect to the meter's floating internal ground. Usually the meter's internal circuits have the same frequency as the auxillary supply voltage.

In the customer's situation where the V1, V2, V3 terminals are disconnected, most likely there is detectable voltage frequency between the Neutral connection on the VN measurement terminal and the meter's internal circuits. Of course when all measurement terminals are disconnected at the meter, there will be no measured frequency.

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore