ION9000 with no Nominal voltage configured

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • ION9000 with no Nominal voltage configured
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Picard Charles_Murison Picard
477
Ramasamy_N
Captain Ramasamy_N Captain
113
Robert_Lee
Admiral Robert_Lee Admiral
92
Mehran_Mehrnia
Captain Mehran_Mehrnia Captain
85
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Solved
sesa74337_bridg
Lt. Commander sesa74337_bridg Lt. Commander
Lt. Commander

Posted: ‎2019-11-27 04:27 AM

0 Likes
2
1424
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-11-27 04:27 AM

ION9000 with no Nominal voltage configured

Hi, All, 

I  need some confirmation for following enquiries

  • If the ION9000 has no nominal voltage and nominal frequency set up (e.g nominal voltage = 0), also, meter internal clock has not be configured, when a voltage spike event happened, will the meter capture any events?
  • When a voltage spike event happens, what information will the meter provide if there is only CT ratio configured in the meter. 
  • Can we use ION Setup to get the power quality events (Sag/Swell/Transient, Comtrade waveforms), disturbance direction detection as well as the 1ms data logging?

Thanks

James R

Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
DanL
Captain DanL Captain
Captain

Posted: ‎2019-11-28 10:54 AM

0 Likes
0
1413
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-11-28 10:54 AM

  • On the ION9000, the nominal voltage is configured in the factory module as "FAC1 Vnominal" (factory default = 120V), while the nominal frequency is configured from the power meter module as "PM1 Nominal Frequency" (factory default = 60Hz).
    • Neither can be set to 0.
    • Power quality alarms that rely on these settings to be configured correctly are disabled by default in the default frameworks.
    • Additionally, the nominal frequency setting affects the harmonic bandwidth (as prescribed in IEC61000-4-30) as well as the default sampling rates used by the meter when line frequency is out of range.
    • Other than the timezone (used for displaying timestamps, but not for storing them), the clock defaults are of little consequence in the context of this question.
  • Both the CT and PT ratios are factory default to 1:1. They affect the scaling of relative current, voltage, power, and energy readings.
    • If the PT ratio mis-configured with the defaults, all voltage, power, and energy readings would need to be post-scaled to read correctly
  • Yes, ION Setup can be configured to read all the data available over ION protocol.

See Answer In Context

Reply
Replies 2
Charles_Murison
Picard Charles_Murison Picard
Picard

Posted: ‎2019-11-27 04:44 PM

0 Likes
1
1418
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-11-27 04:44 PM

Hello James,

 

If the nominal voltage is 0, the sag/swell module is turned off, any events one would expect from the sag/swell module will not be exposed to the meter’s framework including the event log and waveform recorders. The frequency setting does have some significance when the meter checks the half cycle RMS value but in of itself would not prevent the meter from detecting an event. The clock setting would also not prevent the recording of an event, the timestamp logged in the meter may not exactly match the time the event happened.

 

The sag/swell module is off and not able to feed any information like sag/swell durations or magnitudes nor trigger waveform recordings nor does the module write any information to the vent log.

 

Assuming the meter is configured, yes ION Setup can be used to get information from the meter. If the default settings in ION Setup does not include all the data desired, it is possible to augment the configuration. The event details, waveforms,  disturbance direction detection as well as the 1ms data logging are all available with the default configuration.

 

 

Thank you,

Charles

L4 Prime for Advanced metering and Utilities
Reply
DanL
Captain DanL Captain
Captain

Posted: ‎2019-11-28 10:54 AM

0 Likes
0
1414
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-11-28 10:54 AM

  • On the ION9000, the nominal voltage is configured in the factory module as "FAC1 Vnominal" (factory default = 120V), while the nominal frequency is configured from the power meter module as "PM1 Nominal Frequency" (factory default = 60Hz).
    • Neither can be set to 0.
    • Power quality alarms that rely on these settings to be configured correctly are disabled by default in the default frameworks.
    • Additionally, the nominal frequency setting affects the harmonic bandwidth (as prescribed in IEC61000-4-30) as well as the default sampling rates used by the meter when line frequency is out of range.
    • Other than the timezone (used for displaying timestamps, but not for storing them), the clock defaults are of little consequence in the context of this question.
  • Both the CT and PT ratios are factory default to 1:1. They affect the scaling of relative current, voltage, power, and energy readings.
    • If the PT ratio mis-configured with the defaults, all voltage, power, and energy readings would need to be post-scaled to read correctly
  • Yes, ION Setup can be configured to read all the data available over ION protocol.
Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of