ION8800 Communication

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • ION8800 Communication
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Picard Charles_Murison Picard
488
Ramasamy_N
Captain Ramasamy_N Captain
113
Robert_Lee
Admiral Robert_Lee Admiral
92
Mehran_Mehrnia
Captain Mehran_Mehrnia Captain
89
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Metering & Power Quality
Yut
Captain Yut
Captain

Posted: ‎2020-09-23 02:14 AM

0 Likes
4
2224
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-09-23 02:14 AM

ION8800 Communication

I am doing experiment to show and confirm to our customer that the ION8800 has multi access capability.

Using telnet show something strange.

There is DLMS connection but the telnet show Invalid(192.168.2.3) the software Gurux is reading data.

One connection from ION Setup (192.168.2.86). 

One Telnet (192.168.2.86).

One PME(192.168.2.3)

There is one software IED Explorer reading the meter using IEC61850 protocol but not show in Telnet.

If there is any explanation please advice.

Capture.JPG

Labels
  • Labels:
  • ION8000
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic
Replies 4
Anonymous user
Not applicable

Posted: ‎2020-09-28 02:48 AM

0 Likes
0
2216
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-09-28 02:48 AM

Hi, the community members can you help this member, please?  

 

@Charles_Murison do you think you can advise on this topic?

 

Tags (1)
  • Tags:
  • english
Reply
Charles_Murison
Picard Charles_Murison Picard
Picard

Posted: ‎2020-09-28 10:19 AM

0 Likes
2
2212
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-09-28 10:19 AM

Hello Yut,

 

I am having a little trouble getting the ftp working on my ION8800 at home right now so I cannot speak to that aspect directly. When you use the telnet are you actively reading updated values on a schedule with IEC61850 software? Some software will open a connection, request data then close connection. 

 

If you set the telnet to use debug parser and issue command "eds", do you still see invalid?

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities
Tags (1)
  • Tags:
  • english
Reply
Yut
Captain Yut
Captain

Posted: ‎2020-09-29 12:47 AM

0 Likes
0
2209
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-09-29 12:47 AM

For IEC61850 it may open then close the connection as you mention I will study further. The IED Explorer was reading MMXU continuously the Telnet might not be able to capture. I will perform experiment with Telnet option when I'm free. 

Tags (1)
  • Tags:
  • english
Reply
Yut
Captain Yut
Captain

Posted: ‎2020-10-08 12:15 AM

0 Likes
0
2200
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-10-08 12:15 AM

I use EDS command it showed INVALID 

IEC61850 sofware is running but did not show.Telnet Capture.JPG

Tags (1)
  • Tags:
  • english
Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of