ION8800 Communication
I am doing experiment to show and confirm to our customer that the ION8800 has multi access capability.
Using telnet show something strange.
There is DLMS connection but the telnet show Invalid(192.168.2.3) the software Gurux is reading data.
One connection from ION Setup (192.168.2.86).
One Telnet (192.168.2.86).
One PME(192.168.2.3)
There is one software IED Explorer reading the meter using IEC61850 protocol but not show in Telnet.
If there is any explanation please advice.
- Labels:
-
ION8000

Posted: 2020-09-28 02:48 AM
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Hi, the community members can you help this member, please?
@Charles_Murison do you think you can advise on this topic?
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Hello Yut,
I am having a little trouble getting the ftp working on my ION8800 at home right now so I cannot speak to that aspect directly. When you use the telnet are you actively reading updated values on a schedule with IEC61850 software? Some software will open a connection, request data then close connection.
If you set the telnet to use debug parser and issue command "eds", do you still see invalid?
Regards,
Charles
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
For IEC61850 it may open then close the connection as you mention I will study further. The IED Explorer was reading MMXU continuously the Telnet might not be able to capture. I will perform experiment with Telnet option when I'm free.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
I use EDS command it showed INVALID
IEC61850 sofware is running but did not show.