Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Brand Logo
Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
close
  • Community Home
  • Forums
    • By Topic
    • By Topic
      EcoStruxure Building
      • Field Devices Forum
      • SmartConnector Forum
      EcoStruxure Power & Grid
      • Gateways and Energy Servers
      • Metering & Power Quality
      • Protection & Control
      APC UPS, Critical Power, Cooling and Racks
      • APC UPS Data Center & Enterprise Solutions Forum
      • APC UPS for Home and Office Forum
      EcoStruxure IT
      • EcoStruxure IT forum
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • EcoStruxure Geo SCADA Expert Forum
      • Remote Operations Forum
      Industrial Automation
      • Alliance System Integrators Forum
      • AVEVA Plant SCADA Forum
      • CPG Expert Forum DACH
      • EcoStruxure Automation Expert / IEC 61499 Forum
      • Fabrika ve Makina Otomasyonu Çözümleri
      • Harmony Control Customization Forum
      • Industrial Edge Computing Forum
      • Industry Automation and Control Forum
      • Korea Industrial Automation Forum
      • Machine Automation Forum
      • Modicon PAC Forum
      • PLC Club Indonesia
      Schneider Electric Wiser
      • Schneider Electric Wiser Forum
      Power Distribution IEC
      • Eldistribution & Fastighetsautomation
      • Elektrik Tasarım Dağıtım ve Uygulama Çözümleri
      • Paneelbouw & Energie Distributie
      • Power Distribution and Digital
      • Solutions for Motor Management
      • Specifiers Club ZA Forum
      • Електропроектанти България
      Power Distribution NEMA
      • Power Monitoring and Energy Automation NAM
      Power Distribution Software
      • EcoStruxure Power Design Forum
      • LayoutFAST User Group Forum
      Energy & Sustainability Services
      • Green Building Scoring and Certification Forum
      Light and Room Control
      • SpaceLogic C-Bus Forum
      Solutions for your Business
      • Solutions for your Business Forum
      Support
      • Ask the Community
  • Knowledge Center
    • Building Automation Knowledge Base
    • Remote Operations Devices Knowledge Base
    • Geo SCADA Knowledge Base
    • Industrial Automation How-to videos
    • Digital E-books
    • Success Stories Corner
    • EcoStruxure IT Help Center
  • Events & Webinars
    • All Events
    • Innovation Talks
    • Innovation Summit
    • Let's Exchange Series
    • Partner Success
    • Process Automation Talks
    • Technology Partners
  • Ideas
    • EcoStruxure Building
      • EcoStruxure Building Advisor Ideas
      Remote Operations
      • EcoStruxure Geo SCADA Expert Ideas
      • Remote Operations Devices Ideas
      Industrial Automation
      • Modicon Ideas & new features
  • Blogs
    • By Topic
    • By Topic
      EcoStruxure Power & Grid
      • Backstage Access Resources
      EcoStruxure IT
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • Remote Operations Blog
      Industrial Automation
      • Industrie du Futur France
      • Industry 4.0 Blog
      Power Distribution NEMA
      • NEMA Power Foundations Blog
      Energy & Sustainability Services
      • Active Energy Management Blog
      Light and Room Control
      • KNX Blog
      Knowledge Center
      • Digital E-books
      • Geo SCADA Knowledge Base
      • Industrial Automation How-to videos
      • Remote Operations Devices Knowledge Base
      • Success Stories Corner
  • companyImpact

Important Announcement: Community Back to Full Functionality

Dear Members, we are thrilled to announce that our Community is back to full functionality and that posts publication is now enabled again! We appreciate your patience during the last weeks. Learn more about our Community Guidelines. Thank you, Schneider Electric Community Team.

ION8650C current input burden

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Communities
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • ION8650C current input burden
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Picard Charles_Murison Picard
299
Ramasamy_N
Commander Ramasamy_N Commander
75
DanL
Captain DanL Captain
72
Robert_Lee
Captain Robert_Lee Captain
67
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Solved
Marcos_Augusto
Ensign Marcos_Augusto Ensign
Ensign

Posted: ‎2016-10-05 07:28 AM

0 Likes
9
2123
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2016-10-05 07:28 AM

ION8650C current input burden

      Does anybody happen to know why has ION8650C Socket burden rocket from 0,05 to 8VA?

Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
AmyRizner
Ensign AmyRizner Ensign
Ensign

Posted: ‎2016-10-13 12:30 PM

0 Likes
1
2062
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2016-10-13 12:30 PM

Our Marcom team has informed me that this will get fixed in the next revision of the catalog.

As Dan explained, the latest Install Sheets have the correct values.

Hope this helps.

See Answer In Context

Reply
Replies 9
DanL
Captain DanL Captain
Captain

Posted: ‎2016-10-06 10:48 AM

0 Likes
8
2062
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2016-10-06 10:48 AM

The CT input burden of the ION8650 Socket meter is 0.05VA at 5A (0.002 Ohm max).

The power supply burden of the ION8650 meter is approximately 8VA (depends on order option and supply characteristics). The ION8650 can be ordered with an auxillary power cord or with an internal 3-phase supply powered from the voltage measurement terminals.

Reply
Marcos_Augusto
Ensign Marcos_Augusto Ensign
Ensign

Posted: ‎2016-10-06 11:08 AM

0 Likes
4
2062
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2016-10-06 11:08 AM

Hi, Dan. Thanks for your reply. I just got this question from a customer, and he sent me the datasheet tables below.

Considering your explanation, the information really looks a bit confused in the table. I totally understand the customer's surprise.

Take a look...

BR

ION_Comp.jpg

Reply
DanL
Captain DanL Captain
Captain

Posted: ‎2016-10-06 02:22 PM

0 Likes
3
2062
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2016-10-06 02:22 PM

Which installation guide is that from?

The latest I can find is here and looks correct.

http://download.schneider-electric.com/files?p_enDocType=User+guide&p_File_Id=902333793&p_File_Name=...

Reply
Marcos_Augusto
Ensign Marcos_Augusto Ensign
Ensign

Posted: ‎2016-10-07 06:50 AM

0 Likes
2
2062
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2016-10-07 06:50 AM

Actually it is from a catalogue.

You can check by yourself using the following link:

https://schneider-electric.box.com/s/vbj3b1s64a7nv64yxqmwgroq8s0ujctr

BR

Reply
AmyRizner
Ensign AmyRizner Ensign
Ensign

Posted: ‎2016-10-13 12:30 PM

0 Likes
1
2063
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2016-10-13 12:30 PM

Our Marcom team has informed me that this will get fixed in the next revision of the catalog.

As Dan explained, the latest Install Sheets have the correct values.

Hope this helps.

Reply
Marcos_Augusto
Ensign Marcos_Augusto Ensign
Ensign

Posted: ‎2016-10-13 12:45 PM

0 Likes
0
2062
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2016-10-13 12:45 PM

Ok. I just told that to the customer and sent him the 2015 User Guide.

Thank you, Amy and Dan.

BR

Reply
Scott_MCN
Lieutenant Scott_MCN
Lieutenant

Posted: ‎2021-05-20 08:46 AM

0 Likes
2
2013
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-05-20 08:46 AM

Hi Dan,

 

What's the burden for the M8650A0C0E6C7C4A? The datasheet gives a typical and maximum value for socket form factor. 

 

 

Regards,

 

– Scott Clysdale

Tags (1)
  • Tags:
  • english
Reply
DanL
Captain DanL Captain
Captain

Posted: ‎2021-05-20 10:18 AM

0 Likes
1
2011
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-05-20 10:18 AM

I've informed @Sanjeet_Sahota about the errors in the technical datasheet: PLSED310027EN_US

The 22/03/2021 version of this document has the "blade power supply" burden spec moved into the current burden section. 

If there are other documents in error, please let him know.

 

The correct specification is:

Socket Current Class 2/10/20
Input-Current burden: 0.05VA per phase at 5A (2 milliOhms max)

 

Switchboard Current Class 2/10/20
Input-Current burden: 0.05VA per phase at 1A (50 milliOhms max)

 

 

Tags (1)
  • Tags:
  • english
Reply
Sanjeet_Sahota
Lt. Commander Sanjeet_Sahota Lt. Commander
Lt. Commander

Posted: ‎2021-10-29 09:11 AM

1 Like
0
1383
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-10-29 09:11 AM

Hi Everyone,


Just to follow up on this topic.  First off, thanks @DanL for providing the correct information.  This information will be corrected in the latest revision of the technical datasheet being released in a few days. 

Best Regards,

Sanjeet

Tags (1)
  • Tags:
  • english
Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Additional options
You do not have permission to remove this product association.
 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this forum after you log in or create your free account.