ION8650 integrated using IEC-61850, cVal.mag values are in Bad quality and without time stamp

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • ION8650 integrated using IEC-61850, cVal.mag values are in Bad quality and without time stamp
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Picard Charles_Murison Picard
511
Mehran_Mehrnia
Captain Mehran_Mehrnia Captain
115
Ramasamy_N
Captain Ramasamy_N Captain
115
Robert_Lee
Admiral Robert_Lee Admiral
96
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Start a Topic
Solved
Pepz
Crewman Pepz
Crewman

Posted: ‎2025-08-15 03:14 PM

0 Likes
5
243
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-08-15 03:14 PM

ION8650 integrated using IEC-61850, cVal.mag values are in Bad quality and without time stamp

I am integrating ION8650C Power meters to 800xA System DCS using IEC-61850 protocol, I can read almost all the data, but I have problems with all data ending in "cVal.mag" (currents, voltages), becasue when the values of this data change, the changes are automatically displayed but with Bad quality and without time stamp.

Power meter model: M8650C7C0H6E1A0A

File used: SE_ION_8650-C-F01_E2V01.icd

I attached screenshots.

Pepz_0-1755295963071.png

 

 

 

 

Attachments
Screenshots.7z
Labels
  • Labels:
  • ION8000
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Pepz
Crewman Pepz
Crewman

Posted: ‎2025-08-27 03:46 PM

0 Likes
1
136
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-08-27 03:46 PM

Hi Mehran,

 

I have used the default values for the RCB parameters, which are the same as those are you suggest.

Pepz_0-1756334383448.png

 

It seems that the problem is on the 800xA system side, I have requested assistance.

I will let you know if I manage to solve it.

 

Thank you

See Answer In Context

Reply
Replies 5
Mehran_Mehrnia
Captain Mehran_Mehrnia Captain
Captain

Posted: ‎2025-08-18 11:59 AM . Last Modified: ‎2025-08-18 12:15 PM

1 Like
4
234
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-08-18 11:59 AM

Hi @Pepz 

 

Please make sure the dataset includes the Data Attribute Level e.g., cVal.mag, q, t and not just Data Object Level e.g., PhV, A, PPV.

 

In IEC 61850:

Logical Node: e.g., MMXU1
Data Object: e.g., PhV, A, PPV
Data Attribute: e.g., cVal.mag, q, t


If your dataset only includes the Data Object (like PhV or A) without specifying the Data Attribute (like cVal.mag, q and t), the client may not receive the actual measurement values, timestamps, or quality indicators.


You can also use some IED Explorer or IEDScout Tools to confirm whether the issue is with the meter or the 800xA client.

Mehran_Mehrnia_0-1755543646752.png

 

 

Best Regards,

-Mehran

L3 Expert Advanced metering

Reply
Pepz
Crewman Pepz
Crewman

Posted: ‎2025-08-26 10:04 AM

0 Likes
3
158
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-08-26 10:04 AM

Hi Mehran,

 

Thanks for your response.

Initially, I used the total Datasets and RCBs generated for default, without changing anything on the map. The result was that I obtained values that changed automatically but with Bad quality and no timestamp. This only happens with data with values per phase (currents, voltages,...). If I update manually (polling) I can read perfectly: good values, good quality and timestamp, the problem is the automatic update.

Now, I have tried modifying the "MMXU" Dataset to include the Data Attribute Level, but this time I can't see any values. 

In both situations I can see the values with IEC Explorer, with good quality and timestamp. 

I would appreciate it if you could show me an example of "MMXU" Dataset of an ION8650 integrated by IEC61850 from any application you have done before.

 

Pepz_0-1756227836604.png

 

Reply
Mehran_Mehrnia
Captain Mehran_Mehrnia Captain
Captain

Posted: ‎2025-08-27 01:03 PM . Last Modified: ‎2025-08-27 01:05 PM

0 Likes
2
145
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-08-27 01:03 PM

Hi @Pepz 

 

You're welcome. 

 

If manual polling retrieves correct values with good quality and timestamp but automatic updates shows bad quality and no timestamp using default datasets and RCBs, then likely it is due to how the Report Control Blocks (RCBs) and Datasets are configured in the CID file and how they are parsed in 800xA System client.

 

I usually generates the CID file using CET850 and test the result using IED Explorer. What I would suggest is, checking RCB Settings and ensure the RCB has: TrgOps with dchg=true, qchg=true, period=true,

OptFields with timeStamp=true, reasonCode=true, seqNum=true

 

CET850:

Mehran_Mehrnia_0-1756323575199.png

 

editing CID file:

Mehran_Mehrnia_1-1756323974371.png

 

IED Explorer shows correct data, therefore the dataset works in IED Explorer, client 800xA still shows bad quality and no timestamp, please verify if its IEC 61850 parser supports DA-level references.

 

Best Regards,

-Mehran

L3 Expert Advanced metering

Reply
Pepz
Crewman Pepz
Crewman

Posted: ‎2025-08-27 03:46 PM

0 Likes
1
137
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-08-27 03:46 PM

Hi Mehran,

 

I have used the default values for the RCB parameters, which are the same as those are you suggest.

Pepz_0-1756334383448.png

 

It seems that the problem is on the 800xA system side, I have requested assistance.

I will let you know if I manage to solve it.

 

Thank you

Reply
Charles_Murison
Picard Charles_Murison Picard
Picard

Posted: ‎2025-08-28 11:59 AM

0 Likes
0
124
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-08-28 11:59 AM

Hello @Pepz ,

If using a report subscription, the ION8650 meter does not send a timestamp attribute for each measurement, the timestamp of the report is the timestamp for all measurements in the report.

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities
Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore