Ask our Experts
Didn't find what you are looking for? Ask our experts!
New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).
Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.
Search in
Link copied. Please paste this link to share this article on your social media post.
My PrimeRead system is able to access and call the meter each hour with no issues but a second party we work with at the meter site accesses the meter data via TCP Port 502. This is what they said; "
It looks like we can ping the meter and can see that the TCP Port 502 is open. We cannot pull values from the device itself regardless of the pull we are attempting. You would need to contact the manufacturer to troubleshoot it further since the device is not sending us data."
Anyone have any ideas? This issue just started in the last week (10/7/25)
Link copied. Please paste this link to share this article on your social media post.
Hello Charles,
They are getting an error message in their Modpoll stating Reply Timeout on this meter compared to what they normally see and continue to see on a sister meter; -1. I compared both meters for any changes and compared modbus information and Event Logs and I think the issue is with either their connection from their meter to a data logger or the data logger for that meter is having issues. I am going to have them test those non-meter elements and then go from there now that I see that error message. Any ideas are appreciated. Thank you for your help!
Link copied. Please paste this link to share this article on your social media post.
Hello @cchapman_AMP ,
From description alone I cannot say what is happening. Did they give you any details about "We cannot pull values"? Are they getting N/A values, Modbus exceptions, other? Did you check that meter's settings or Modbus slave modules have not been changed? Is your PrimeRead system also using Modbus on Port 502?
If more troubleshooting is needed, likely you will want to contact your local technical support and start a case.
Regards,
Charles
Link copied. Please paste this link to share this article on your social media post.
Hello Charles,
They are getting an error message in their Modpoll stating Reply Timeout on this meter compared to what they normally see and continue to see on a sister meter; -1. I compared both meters for any changes and compared modbus information and Event Logs and I think the issue is with either their connection from their meter to a data logger or the data logger for that meter is having issues. I am going to have them test those non-meter elements and then go from there now that I see that error message. Any ideas are appreciated. Thank you for your help!
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.