Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

ION8650 Meter Is Not Allowing Data Read Even Though TCP Port 502 Is Open

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • Re: ION8650 Meter Is Not Allowing Data Read Even Though TCP Port 502 Is Open
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Charles_Murison Champion
571
Mehran_Mehrnia
Mehran_Mehrnia Champion
202
Ramasamy_N
Ramasamy_N Champion
115
View All

Recommended Forums

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Start a Topic
Solved
cchapman_AMP
cchapman_AMP
Contributor

Posted: ‎2025-10-07 08:06 AM

0 Likes
2
1846
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-10-07 08:06 AM

ION8650 Meter Is Not Allowing Data Read Even Though TCP Port 502 Is Open

My PrimeRead system is able to access and call the meter each hour with no issues but a second party we work with at the meter site accesses the meter data via TCP Port 502.  This is what they said; "

It looks like we can ping the meter and can see that the TCP Port 502 is open. We cannot pull values from the device itself regardless of the pull we are attempting. You would need to contact the manufacturer to troubleshoot it further since the device is not sending us data."

 

Anyone have any ideas?  This issue just started in the last week (10/7/25)

 

Labels
  • Labels:
  • ION Downloads
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
cchapman_AMP
cchapman_AMP
Contributor

Posted: ‎2025-10-09 05:12 AM

0 Likes
0
1812
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-10-09 05:12 AM

Hello Charles,

They are getting an error message in their Modpoll stating Reply Timeout on this meter compared to what they normally see and continue to see on a sister meter; -1.  I compared both meters for any changes and compared modbus information and Event Logs and I think the issue is with either their connection from their meter to a data logger or the data logger for that meter is having issues.  I am going to have them test those non-meter elements and then go from there now that I see that error message.  Any ideas are appreciated.  Thank you for your help!

See Answer In Context

Reply
Replies 2
Charles_Murison
Charles_Murison Champion
Champion

Posted: ‎2025-10-08 08:50 AM

0 Likes
1
1841
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-10-08 08:50 AM

Hello @cchapman_AMP ,

 

From description alone I cannot say what is happening. Did they give you any details about "We cannot pull values"? Are they getting N/A values, Modbus exceptions, other? Did you check that meter's settings or Modbus slave modules have not been changed? Is your PrimeRead system also using Modbus on Port 502?

 

If more troubleshooting is needed, likely you will want to contact your local technical support and start a case. 

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities
Reply
cchapman_AMP
cchapman_AMP
Contributor

Posted: ‎2025-10-09 05:12 AM

0 Likes
0
1813
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-10-09 05:12 AM

Hello Charles,

They are getting an error message in their Modpoll stating Reply Timeout on this meter compared to what they normally see and continue to see on a sister meter; -1.  I compared both meters for any changes and compared modbus information and Event Logs and I think the issue is with either their connection from their meter to a data logger or the data logger for that meter is having issues.  I am going to have them test those non-meter elements and then go from there now that I see that error message.  Any ideas are appreciated.  Thank you for your help!

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore