【ION9000】Maximum depth of saved log data

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • 【ION9000】Maximum depth of saved log data
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Picard Charles_Murison Picard
517
Mehran_Mehrnia
Admiral Mehran_Mehrnia Admiral
126
Ramasamy_N
Captain Ramasamy_N Captain
115
Robert_Lee
Admiral Robert_Lee Admiral
96
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Start a Topic
Solved
Miyai
Lieutenant Miyai
Lieutenant

Posted: ‎2025-10-06 11:29 PM

0 Likes
2
109
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-10-06 11:29 PM

【ION9000】Maximum depth of saved log data

Hello,

 

I'd like some advice on a customer question.
We have started experiments with ION9000, but the test period will be long.

-------------------------------------------------------------------------------------

Is there a limit to the amount of log data that can be acquired?

I changed logging settings on the ION9000.
・Log interval 1 min
・Log Depth 35 days
(24H x 60/1min x35 days =50,400)
I have confirmed that there is sufficient log memory remaining.


When I output the log data from the IONsetup data screens, The number of items output was 36,6000.
This means 23.3 days of data.
(24H x 60/1min x23.333 days =33,600)

 

Does this mean the max limit for storing log data is 36,600?
Or is it because the maximum number of images that can be displayed in IONsetup is 36,600?

I tried logging for several days, but the log output was 23,333 days.

 

 

Best regards,

Miyai

Labels
  • Labels:
  • ION9000
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Mehran_Mehrnia
Admiral Mehran_Mehrnia Admiral
Admiral

Posted: ‎2025-10-07 08:03 AM

1 Like
1
98
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-10-07 08:03 AM

Hi @Miyai 

 

This is not a limitation of the meter, but rather a display/export limit within ION Setup. Here's how it works:

 

Regarding ION9000 Meter logging capacity, the ION9000 meter itself can store much more than 33,600 records. Each Data Recorder in the ION9000 has a maximum depth size of 10 MB (10,485,760 bytes).

 

For example, a Data Recorder configured with 16 inputs can store up to approximately 97,089 records.

Note: As the number of input sources increases (up to 50 linked sources in firmware version V4.6) the allowable depth value decreases accordingly.


The actual logging capacity depends on:

- The log depth configured in the Data Recorder module.
- The available memory in the meter.
- The number of parameters being logged.

A configuration such as 1-minute intervals over 35 days (i.e., 50,400 records) is valid as long as sufficient memory is available.

 

Regarding ION Setup Display/Export Limit, the 33,600 record limit you're seeing is not a limitation of the meter, but rather a display/export limit in ION Setup. This limit can be manually increased by editing the .pml file associated with the data recorder view.


To increase the limit, navigate to:
C:\Program Files (x86)\Schneider Electric\ION Setup\Tables\<MeterType>\<TemplateVersion>\Data Recorders
In this example:
C:\Program Files (x86)\Schneider Electric\ION Setup\Tables\PML9000\Standard V4.6.0 Default\Data Recorders


Open the relevant .pml file (e.g., Revenue Log.pml) using Notepad, and locate and modify the line: ROWS=33600

Mehran_Mehrnia_0-1759849403716.png

 

You can increase this value depending on your needs (e.g., ROWS=50400 for 35 days of 1-minute data).

Save the file and reconnect the meter in ION Setup.

 

Please note that increasing the number of rows may impact performance, especially when displaying or exporting large datasets.

 

Best Regards,

-Mehran

L3 Expert Advanced metering

See Answer In Context

Reply
Replies 2
Mehran_Mehrnia
Admiral Mehran_Mehrnia Admiral
Admiral

Posted: ‎2025-10-07 08:03 AM

1 Like
1
99
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-10-07 08:03 AM

Hi @Miyai 

 

This is not a limitation of the meter, but rather a display/export limit within ION Setup. Here's how it works:

 

Regarding ION9000 Meter logging capacity, the ION9000 meter itself can store much more than 33,600 records. Each Data Recorder in the ION9000 has a maximum depth size of 10 MB (10,485,760 bytes).

 

For example, a Data Recorder configured with 16 inputs can store up to approximately 97,089 records.

Note: As the number of input sources increases (up to 50 linked sources in firmware version V4.6) the allowable depth value decreases accordingly.


The actual logging capacity depends on:

- The log depth configured in the Data Recorder module.
- The available memory in the meter.
- The number of parameters being logged.

A configuration such as 1-minute intervals over 35 days (i.e., 50,400 records) is valid as long as sufficient memory is available.

 

Regarding ION Setup Display/Export Limit, the 33,600 record limit you're seeing is not a limitation of the meter, but rather a display/export limit in ION Setup. This limit can be manually increased by editing the .pml file associated with the data recorder view.


To increase the limit, navigate to:
C:\Program Files (x86)\Schneider Electric\ION Setup\Tables\<MeterType>\<TemplateVersion>\Data Recorders
In this example:
C:\Program Files (x86)\Schneider Electric\ION Setup\Tables\PML9000\Standard V4.6.0 Default\Data Recorders


Open the relevant .pml file (e.g., Revenue Log.pml) using Notepad, and locate and modify the line: ROWS=33600

Mehran_Mehrnia_0-1759849403716.png

 

You can increase this value depending on your needs (e.g., ROWS=50400 for 35 days of 1-minute data).

Save the file and reconnect the meter in ION Setup.

 

Please note that increasing the number of rows may impact performance, especially when displaying or exporting large datasets.

 

Best Regards,

-Mehran

L3 Expert Advanced metering

Reply
Miyai
Lieutenant Miyai
Lieutenant

Posted: ‎2025-10-08 02:10 AM

0 Likes
0
80
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-10-08 02:10 AM

Hi, @Mehran_Mehrnia 

 

Thank you for your support.
I changed IONsetup settings and confirmed changes in the log output.

 

Best regards,

Miyai

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore