ION8600 - introducing a delay in sag/swell alarm

Metering & Power Quality

Collaborate with multiple experts and discuss various topics about Power Meters and Power Quality. From design & implementation to troubleshooting and more, get support from experts and share your experiences by subscribing to the Schneider Electric Exchange forum today.

Solved
sesa10844_bridg
Lt. Commander Lt. Commander
Lt. Commander
0 Likes
2
217

ION8600 - introducing a delay in sag/swell alarm

In the ION8600 meter, is it possible to add a delay in the Sag/Swell Module?  A customer wants to trigger a sag/swell alarm only if the voltage falls below 80% of nominal for 80ms or more.  As I understand it, the Sag/Swell module does not allow for any delay, and the Relative Setpoint Module does not operate at a high enough speed to monitor Sag/Swells.  Is this accurate?  Are there any workarounds?  Before we tell the customer that we can't do it, I want to make sure we've covered all of our bases.  Thanks!

Tags (2)

Accepted Solutions
jimbradley
Schneider Alumni (Retired)
Schneider Alumni (Retired)
0 Likes
1
185

Re: ION8600 - introducing a delay in sag/swell alarm

Hi Daniel,

As far as I can see only the normal Setpoint Module would work here.  TheSag/Swell, Signal Limit Evaluation, and Disturbance Analyzer modules all are value driven with no time filter.  As you mentioned the Relative Setpoint no longer runs in high speed mode.

I would argue though that the solution is not at the device level but at the reporting level.  Since the "standard" PQ report has to analysis for event duration anyway shouldn't it possible to modify it so that there is a filter where min event time could be used and the report ignores short duration events ?

Sounds like something for et al.

Jim

See Answer In Context

2 Replies 2
jimbradley
Schneider Alumni (Retired)
Schneider Alumni (Retired)
0 Likes
1
186

Re: ION8600 - introducing a delay in sag/swell alarm

Hi Daniel,

As far as I can see only the normal Setpoint Module would work here.  TheSag/Swell, Signal Limit Evaluation, and Disturbance Analyzer modules all are value driven with no time filter.  As you mentioned the Relative Setpoint no longer runs in high speed mode.

I would argue though that the solution is not at the device level but at the reporting level.  Since the "standard" PQ report has to analysis for event duration anyway shouldn't it possible to modify it so that there is a filter where min event time could be used and the report ignores short duration events ?

Sounds like something for et al.

Jim

Hal_Etheridge
Janeway Janeway
Janeway
0 Likes
0
185

Re: ION8600 - introducing a delay in sag/swell alarm

Doing this at the reporting level also has the advantages that:

- only a single location in the system needs to be configured (the SW) instead of all the devices individually

- it is easy to change the threshold in the future (and retroactively if necessary) to reduce or increase the sensitivity of the system to PQ events

Generally, when an ION module is connected to a High Speed register (like a output from Sag/Swell module) then the module will run at high speed.  There are exceptions though where the module will only run at the "low speed" or one second execution period regardless of the types of inputs.  Unfortunately I am not familiar enough with the specific modules above to know if they are one of the exceptions or not.