Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Brand Logo
Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
close
  • Community Home
  • Forums
    • By Topic
    • By Topic
      EcoStruxure Building
      • Field Devices Forum
      • SmartConnector Forum
      EcoStruxure Power & Grid
      • Gateways and Energy Servers
      • Metering & Power Quality
      • Protection & Control
      APC UPS, Critical Power, Cooling and Racks
      • APC UPS Data Center & Enterprise Solutions Forum
      • APC UPS for Home and Office Forum
      EcoStruxure IT
      • EcoStruxure IT forum
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • EcoStruxure Geo SCADA Expert Forum
      • Remote Operations Forum
      Industrial Automation
      • Alliance System Integrators Forum
      • AVEVA Plant SCADA Forum
      • CPG Expert Forum DACH
      • EcoStruxure Automation Expert / IEC 61499 Forum
      • Fabrika ve Makina Otomasyonu Çözümleri
      • Harmony Control Customization Forum
      • Industrial Edge Computing Forum
      • Industry Automation and Control Forum
      • Korea Industrial Automation Forum
      • Machine Automation Forum
      • Modicon PAC Forum
      • PLC Club Indonesia
      Schneider Electric Wiser
      • Schneider Electric Wiser Forum
      Power Distribution IEC
      • Eldistribution & Fastighetsautomation
      • Elektrik Tasarım Dağıtım ve Uygulama Çözümleri
      • Paneelbouw & Energie Distributie
      • Power Distribution and Digital
      • Solutions for Motor Management
      • Specifiers Club ZA Forum
      • Електропроектанти България
      Power Distribution NEMA
      • Power Monitoring and Energy Automation NAM
      Power Distribution Software
      • EcoStruxure Power Design Forum
      • LayoutFAST User Group Forum
      Energy & Sustainability Services
      • Green Building Scoring and Certification Forum
      Light and Room Control
      • SpaceLogic C-Bus Forum
      Solutions for your Business
      • Solutions for your Business Forum
      Support
      • Ask the Community
  • Knowledge Center
    • Building Automation Knowledge Base
    • Remote Operations Devices Knowledge Base
    • Geo SCADA Knowledge Base
    • Industrial Automation How-to videos
    • Digital E-books
    • Success Stories Corner
    • EcoStruxure IT Help Center
  • Events & Webinars
    • All Events
    • Innovation Talks
    • Innovation Summit
    • Let's Exchange Series
    • Partner Success
    • Process Automation Talks
    • Technology Partners
  • Ideas
    • EcoStruxure Building
      • EcoStruxure Building Advisor Ideas
      Remote Operations
      • EcoStruxure Geo SCADA Expert Ideas
      • Remote Operations Devices Ideas
      Industrial Automation
      • Modicon Ideas & new features
  • Blogs
    • By Topic
    • By Topic
      EcoStruxure Power & Grid
      • Backstage Access Resources
      EcoStruxure IT
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • Remote Operations Blog
      Industrial Automation
      • Industrie du Futur France
      • Industry 4.0 Blog
      Power Distribution NEMA
      • NEMA Power Foundations Blog
      Energy & Sustainability Services
      • Active Energy Management Blog
      Light and Room Control
      • KNX Blog
      Knowledge Center
      • Digital E-books
      • Geo SCADA Knowledge Base
      • Industrial Automation How-to videos
      • Remote Operations Devices Knowledge Base
      • Success Stories Corner
  • companyImpact

Important Announcement: Community Back to Full Functionality

Dear Members, we are thrilled to announce that our Community is back to full functionality and that posts publication is now enabled again! We appreciate your patience during the last weeks. Learn more about our Community Guidelines. Thank you, Schneider Electric Community Team.

ION7650 Downstream Waveform capture

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Communities
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • ION7650 Downstream Waveform capture
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Picard Charles_Murison Picard
299
Ramasamy_N
Commander Ramasamy_N Commander
75
DanL
Captain DanL Captain
72
Robert_Lee
Captain Robert_Lee Captain
67
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Solved
sesa74337_bridg
Lt. Commander sesa74337_bridg Lt. Commander
Lt. Commander

Posted: ‎2014-11-12 04:21 AM

0 Likes
6
1490
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2014-11-12 04:21 AM

ION7650 Downstream Waveform capture

Hi,

Please find the attached Sag/Swell Log from ION7650 meter. My question is why only the Upstream Disturbance Waveform has been recorded, the downstream disturbance just a event log? Is the meter set to only log High Confidence Events? Is that a way to configure it records all downstream waveform as well?

Thanks,

James

Attachments
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
sesa56307_bridg
Lieutenant JG sesa56307_bridg Lieutenant JG
Lieutenant JG

Posted: ‎2014-11-12 01:15 PM

3 Likes
3
1368
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2014-11-12 01:15 PM

Hi James,

There should be no correlation between the Disturbance Direction Detection result (upstream/downstream) or confidence (high/medium/low) and the logging of a waveform file.  Looking at the attached screen capture, I see six different times when there were voltage waveform captures.  Each of those times corresponds to an event (with the same timestamp) indicating that a Sag/Swell disturbance either started or ended.  In each case, there is a second event when the disturbance starts (with the same timestamp), indicating the result of the Disturbance Direction analysis.  It looks like the software happens to show the waveform records aligned on the same row with the Disturbance Direction event, but they are more accurately triggered by the Sag/Swell event (shown in the next row but with the same timestamp).  I think it is just a coincidence that each of these three sag/swell events was detected as being Upstream with High confidence.

Waveform captures are triggered within the ION framework, and there is a set of waveform recorders in the default framework associated with sag/swell events.  These recorders are triggered whenever the Sag/Swell module detects the start or end of a disturbance.  That is why the waveforms are aligned with a sag/swell start or end event here.  Those same triggers are used in the ION framework to initiate the Disturbance Direction analysis.  The default ION framework meets the needs of many customers (and with this explanation maybe it is okay for you too?).  But if you are interested in further customization to how waveform records are triggered, ION is certainly very configurable, and I'm sure we can help you understand your options.

I do not fully understand why there are many Disturbance Direction events that do not seem to be aligned with any Sag/Swell event.  To understand this, we would need to dig a little deeper into your system.  Maybe those ones are caused by Transient events, but the Transient events are filtered out of this view in software (if it's intended to be a Sag/Swell log)?

Best regards,

David

See Answer In Context

Reply
Replies 6
Tom_Stevenson
Picard Tom_Stevenson Picard
Picard

Posted: ‎2014-11-12 09:05 AM

0 Likes
0
1368
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2014-11-12 09:05 AM

- can you help with some insight here?


Thanks


Tom

Reply
Matt_Curry
Administrator Matt_Curry Administrator
Administrator

Posted: ‎2014-11-12 09:25 AM

0 Likes
0
1368
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2014-11-12 09:25 AM

Just moving to the Power Monitoring Hardware Community.

Reply
sesa56307_bridg
Lieutenant JG sesa56307_bridg Lieutenant JG
Lieutenant JG

Posted: ‎2014-11-12 01:15 PM

3 Likes
3
1369
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2014-11-12 01:15 PM

Hi James,

There should be no correlation between the Disturbance Direction Detection result (upstream/downstream) or confidence (high/medium/low) and the logging of a waveform file.  Looking at the attached screen capture, I see six different times when there were voltage waveform captures.  Each of those times corresponds to an event (with the same timestamp) indicating that a Sag/Swell disturbance either started or ended.  In each case, there is a second event when the disturbance starts (with the same timestamp), indicating the result of the Disturbance Direction analysis.  It looks like the software happens to show the waveform records aligned on the same row with the Disturbance Direction event, but they are more accurately triggered by the Sag/Swell event (shown in the next row but with the same timestamp).  I think it is just a coincidence that each of these three sag/swell events was detected as being Upstream with High confidence.

Waveform captures are triggered within the ION framework, and there is a set of waveform recorders in the default framework associated with sag/swell events.  These recorders are triggered whenever the Sag/Swell module detects the start or end of a disturbance.  That is why the waveforms are aligned with a sag/swell start or end event here.  Those same triggers are used in the ION framework to initiate the Disturbance Direction analysis.  The default ION framework meets the needs of many customers (and with this explanation maybe it is okay for you too?).  But if you are interested in further customization to how waveform records are triggered, ION is certainly very configurable, and I'm sure we can help you understand your options.

I do not fully understand why there are many Disturbance Direction events that do not seem to be aligned with any Sag/Swell event.  To understand this, we would need to dig a little deeper into your system.  Maybe those ones are caused by Transient events, but the Transient events are filtered out of this view in software (if it's intended to be a Sag/Swell log)?

Best regards,

David

Reply
sesa74337_bridg
Lt. Commander sesa74337_bridg Lt. Commander
Lt. Commander

Posted: ‎2014-11-17 12:01 AM

0 Likes
2
1368
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2014-11-17 12:01 AM

Hi, David,

Thank you for your reply. I have attached the detailed records and the waveforms from the Site ION7650 Main Supply Meter. It seems the sag/swell Waveform has been detected and recorded every weekday at 7:26 am and 8:06 am. Is that something we can do the further investigation? Also, I have the remote access, if possible, we can schedule a time to have a quick look my settings on the ION7650 Meter.

Thanks,

Regards,

James

Attachments
Reply
sesa56307_bridg
Lieutenant JG sesa56307_bridg Lieutenant JG
Lieutenant JG

Posted: ‎2014-11-17 03:16 PM

1 Like
1
1368
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2014-11-17 03:16 PM

Hi James,

These are some interesting records, and it does seem that there are some PQ events that often occur at the same time of day.  It is beyond my range of expertise to comment on what might be the cause, and how big a concern it is for this system.  I recommend that you engage with someone from our services team who should be better equipped to help analyze these results, and to comment on the implications for this specific installation.  Maybe others in the Solutions Forum have ideas to contribute?  Depending on the cause, I know that we have a number of solutions from our PQ business to help mitigate PQ issues like this.

I am interested to follow this investigation, to understand the cause and the steps we recommend (if any).  But unfortunately, I don't have enough experience to suggest possible causes.

Best regards,

David

Reply
sesa74337_bridg
Lt. Commander sesa74337_bridg Lt. Commander
Lt. Commander

Posted: ‎2014-11-17 04:01 PM

0 Likes
0
1368
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2014-11-17 04:01 PM

Thank you very much for your help, David

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Additional options
You do not have permission to remove this product association.
 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this forum after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2023 Schneider Electric, Inc