[ION7650] Analog output concrete question.

Metering & Power Quality

Collaborate with multiple experts and discuss various topics about Power Meters and Power Quality. From design & implementation to troubleshooting and more, get support from experts and share your experiences by subscribing to the Schneider Electric Exchange forum today.

skkim_isama_net
Lieutenant | EcoXpert Master Lieutenant | EcoXpert Master
Lieutenant | EcoXpert Master
0 Likes
1
152

[ION7650] Analog output concrete question.

Hi. PME Team.

This is basic question ION7650 analog output.

Plant site .

헤더 3헤더 4
1

analog out setting : 0~1000[A] : 4-20mA , completed 2 years ago.

2If the measurement case 1,200[A],  how to analog output card  value.

sorry, I don't have sample demo kit.

Tags (1)
1 Reply 1
Charles_Murison
Picard Picard
Picard
0 Likes
0
136

Re: [ION7650] Analog output concrete question.

Zero scale would be -250

Full scale would be 1000

If input > fullscale, output would be full scale.

L4 Prime for Advanced metering and Utilities