Ask our Experts
Didn't find what you are looking for? Ask our experts!
New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).
Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.
Search in
Please select a country to continue with beta search.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Hello @Mohamed.ElShazly ,
The answer is, it depends. There is a lot of details missing, how are the meters connected, are there other software/devices connected to the meter, etc?
Assuming Ethernet connected meters on the same network with no firewalls and enough connections available. Yes you can do this with modbus. The 2 ION7650 meters you want to read from will be configured as modbus servers. The one ION7650 meter displaying the combined data would be modbus client. There are KBs and user guides on how to setup ION7650 meter as both modbus server and client (may be called master slave).
Then in one ION7650 meter, would develop in framework links from modbus device module to Arithmetic module where calculation would combine measurements.
If you need all ION7650 meters to read from other 2 ION7650 meters, you would need 2 connections free per meter. ION7650 meter can support having more than 1 modbus client.
Regards,
Charles
Link copied. Please paste this link to share this article on your social media post.
Hello @Mohamed.ElShazly ,
The answer is, it depends. There is a lot of details missing, how are the meters connected, are there other software/devices connected to the meter, etc?
Assuming Ethernet connected meters on the same network with no firewalls and enough connections available. Yes you can do this with modbus. The 2 ION7650 meters you want to read from will be configured as modbus servers. The one ION7650 meter displaying the combined data would be modbus client. There are KBs and user guides on how to setup ION7650 meter as both modbus server and client (may be called master slave).
Then in one ION7650 meter, would develop in framework links from modbus device module to Arithmetic module where calculation would combine measurements.
If you need all ION7650 meters to read from other 2 ION7650 meters, you would need 2 connections free per meter. ION7650 meter can support having more than 1 modbus client.
Regards,
Charles
Link copied. Please paste this link to share this article on your social media post.
Hello Charles
Thank you for your response
the meters is connected via Ethernet and not connected to any software
Link copied. Please paste this link to share this article on your social media post.
Hello @Mohamed.ElShazly ,
Then you should be able to setup modbus mastering on ION7650 meter to do what you are wanting.
Regards,
Charles
Link copied. Please paste this link to share this article on your social media post.
Would you please share the instructions to setup modbus mastering?
Link copied. Please paste this link to share this article on your social media post.
Hello @Mohamed.ElShazly ,
You can find some instructions with https://www.se.com/ca/en/faqs/FA309352/, for details on modules you can refer to ION reference https://www.se.com/us/en/download/document/7EN02-0290/.
Regards,
Charles
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.