Continue
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • My Subscriptions
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

ION setup - Complete data set download from a meter

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • ION setup - Complete data set download from a meter
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Charles_Murison Champion
582
Mehran_Mehrnia
Mehran_Mehrnia Champion
216
Ramasamy_N
Ramasamy_N Champion
117
View All

Recommended Forums

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Start a Topic
Solved
Grant_IPACS
Grant_IPACS
Mentor

Posted: ‎2020-04-13 12:21 AM . Last Modified: ‎2020-04-22 01:00 AM

0 Likes
4
4590
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-04-13 12:21 AM

ION setup - Complete data set download from a meter

Hi All,

 

Maybe i'm missing something, but is there a way to do a complete download / extraction of ALL log files and waveforms, etc from a single device, with only a couple of mouse clicks?

 

This seems like a pretty obvious feature for such a mature platform to be missing.

 

The only way i see this is possible today is going to each log file, and copy / paste into excel or similar.

There is a risk that someone may not click on each log file, and data is then lost forever.

 

Reason i ask is we have a client that has asked us to alter every meters logging interval, and in doing this, it prompts us all log data may be lost, and a backup is recommended.

 

There are many meters that make up this project, some from before our time on site, and we don't seem to have the config password to access some meters, and the building manager doesn't know where to start, as she has only been in the position 18 months and cant seem to find them in any obvious location.

 

So i guess its really 2 questions, with the second, how to crack passwords...

 

Thanks 

 

Grant

 

 

Regards

Grant
Labels
  • Labels:
  • ION Setup
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Robert_Lee
Robert_Lee Champion
Champion

Posted: ‎2020-04-14 12:00 PM

0 Likes
0
4578
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-04-14 12:00 PM

The data collection wizard should attempt to collect all available log data for that *ONE* device given what available data is on the device.  It's primary purpose however is to allow you to push that data into a PME system.

ION Setup is not an automated data collection tool.  It's primarily a device configuration tool which has many various other features which we provide *FREE* of charge.


PME on the other hand is a data collection system which will automatically store device data shortly after it occurs which users have to license per device in their system.  It sounds like if the data is important to be collected, then the user should consider this route.

Also most of the non-ION devices you listed do not support any type of file-based storage mechanism using ION Setup (such as the lower end products like PM5xxx and iEM products).

See Answer In Context

Reply
Replies 4
Charles_Murison
Charles_Murison Champion
Champion

Posted: ‎2020-04-13 03:53 PM

0 Likes
3
4585
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-04-13 03:53 PM

Hello @Grant_IPACS

 

A little more information is needed like, what version of ION Setup you have, what meter types and firmware version.

 

For the data collection, have you looked at Setup Assistant -> Reports -> Data Collection?

This will write information into an XML file. 

 

For meter password, different story. With increased cyber security, may of the old ways of accessing a meter have long since been closed off. Even options like brute force trial and error have lockouts now. It is possible that when programming the meters, whoever did the work saved the configuration file?

 

Charles

L4 Prime for Advanced metering and Utilities
Reply
Grant_IPACS
Grant_IPACS
Mentor

Posted: ‎2020-04-14 12:38 AM

0 Likes
2
4583
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-04-14 12:38 AM

Hi and thanks Charles,

 

latest ION setup (? V3.2)

 

i did try that data collection thing... it ran for a few hours, and i got a tiny xml file that seemed useless, maybe i did something wrong?

 

meters are 7650, 9000, 8000, 5560, 5350, iem 3255's.

 

i think the integration  was not one single integrator, possibly many over time... some have defaults,. some do not.

 

BR 

Grant

Regards

Grant
Reply
Robert_Lee
Robert_Lee Champion
Champion

Posted: ‎2020-04-14 12:00 PM

0 Likes
0
4578
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-04-14 12:00 PM

The data collection wizard should attempt to collect all available log data for that *ONE* device given what available data is on the device.  It's primary purpose however is to allow you to push that data into a PME system.

ION Setup is not an automated data collection tool.  It's primarily a device configuration tool which has many various other features which we provide *FREE* of charge.


PME on the other hand is a data collection system which will automatically store device data shortly after it occurs which users have to license per device in their system.  It sounds like if the data is important to be collected, then the user should consider this route.

Also most of the non-ION devices you listed do not support any type of file-based storage mechanism using ION Setup (such as the lower end products like PM5xxx and iEM products).

Reply
Charles_Murison
Charles_Murison Champion
Champion

Posted: ‎2020-04-14 01:20 PM

0 Likes
0
4577
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-04-14 01:20 PM

Hello Grant.

 

ION Setup has a numbering system besides just V 3.2, you would see a series of numbers afterwards, like 20091. I cannot speak to the  5560, 5350, iem 3255's meters, but with the 7650, 9000, 8000, you should be able to extract the data. If you are having trouble, I recommend contacting technical support. Be sure to include a screenshot of ION Setup options, an extract of a data recorder and the .xml file generated.

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities
Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore