Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Brand Logo
Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
close
  • Community Home
  • Forums
    • By Topic
    • By Topic
      EcoStruxure Building
      • Field Devices Forum
      • SmartConnector Forum
      EcoStruxure Power & Grid
      • Gateways and Energy Servers
      • Metering & Power Quality
      • Protection & Control
      APC UPS, Critical Power, Cooling and Racks
      • APC UPS Data Center & Enterprise Solutions Forum
      • APC UPS for Home and Office Forum
      EcoStruxure IT
      • EcoStruxure IT forum
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • EcoStruxure Geo SCADA Expert Forum
      • Remote Operations Forum
      Industrial Automation
      • Alliance System Integrators Forum
      • AVEVA Plant SCADA Forum
      • CPG Expert Forum DACH
      • EcoStruxure Automation Expert / IEC 61499 Forum
      • Fabrika ve Makina Otomasyonu Çözümleri
      • Harmony Control Customization Forum
      • Industrial Edge Computing Forum
      • Industry Automation and Control Forum
      • Korea Industrial Automation Forum
      • Machine Automation Forum
      • Modicon PAC Forum
      • PLC Club Indonesia
      Schneider Electric Wiser
      • Schneider Electric Wiser Forum
      Power Distribution IEC
      • Eldistribution & Fastighetsautomation
      • Elektrik Tasarım Dağıtım ve Uygulama Çözümleri
      • Paneelbouw & Energie Distributie
      • Power Distribution and Digital
      • Solutions for Motor Management
      • Specifiers Club ZA Forum
      • Електропроектанти България
      Power Distribution NEMA
      • Power Monitoring and Energy Automation NAM
      Power Distribution Software
      • EcoStruxure Power Design Forum
      • LayoutFAST User Group Forum
      Energy & Sustainability Services
      • Green Building Scoring and Certification Forum
      Light and Room Control
      • SpaceLogic C-Bus Forum
      Solutions for your Business
      • Solutions for your Business Forum
      Support
      • Ask the Community
  • Knowledge Center
    • Building Automation Knowledge Base
    • Remote Operations Devices Knowledge Base
    • Geo SCADA Knowledge Base
    • Industrial Automation How-to videos
    • Digital E-books
    • Success Stories Corner
    • EcoStruxure IT Help Center
  • Events & Webinars
    • All Events
    • Innovation Talks
    • Innovation Summit
    • Let's Exchange Series
    • Partner Success
    • Process Automation Talks
    • Technology Partners
  • Ideas
    • EcoStruxure Building
      • EcoStruxure Building Advisor Ideas
      Remote Operations
      • EcoStruxure Geo SCADA Expert Ideas
      • Remote Operations Devices Ideas
      Industrial Automation
      • Modicon Ideas & new features
  • Blogs
    • By Topic
    • By Topic
      EcoStruxure Power & Grid
      • Backstage Access Resources
      EcoStruxure IT
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • Remote Operations Blog
      Industrial Automation
      • Industrie du Futur France
      • Industry 4.0 Blog
      Power Distribution NEMA
      • NEMA Power Foundations Blog
      Energy & Sustainability Services
      • Active Energy Management Blog
      Light and Room Control
      • KNX Blog
      Knowledge Center
      • Digital E-books
      • Geo SCADA Knowledge Base
      • Industrial Automation How-to videos
      • Remote Operations Devices Knowledge Base
      • Success Stories Corner
  • companyImpact

Important Announcement: Protecting our Community from Spam Events

Dear Members, we apologize for any disruption or inconvenience caused by the recent spam incidents, and we want to assure you that our dedicated team is actively investigating each reported instance of spam and implementing robust measures to mitigate the impact. Learn more on Spams Mitigation Guidelines

Thank you,

Schneider Electric Community Team

ION Regular Power meter values - calculation method?

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Communities
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • ION Regular Power meter values - calculation method?
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Picard Charles_Murison Picard
292
Ramasamy_N
Commander Ramasamy_N Commander
75
DanL
Captain DanL Captain
71
Robert_Lee
Captain Robert_Lee Captain
67
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Solved
conradvr_hexeis
Lieutenant | EcoXpert Master conradvr_hexeis Lieutenant | EcoXpert Master
Lieutenant | EcoXpert Master

Posted: ‎2020-04-14 11:49 PM

0 Likes
4
702
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-04-14 11:49 PM

ION Regular Power meter values - calculation method?

In the ION power quality meters ION7650, ION7400, PM8000 and ION9000 the regular Power Meter module updates the outputs once per second.

 

Are the output values of this module the mean of all cycles within the 1 second interval or the RMS value of the last cycle within the 1 second interval?  For example in a 50Hz system is the Phase A current the:

 

1. Mean of the last 50 cycles OR

2. The snapshot value of the last cycle

 

We have an application that needs to calculate and record the 1 second mean per phase currents in ION7650 and ION9000 devices.

Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Charles_Murison
Picard Charles_Murison Picard
Picard

Posted: ‎2020-04-15 08:34 AM

0 Likes
0
697
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-04-15 08:34 AM

Hello @conradvr_hexeis ,

 

In the power meter module, the current and voltage value is the RMS over the entire 1 second interval.

 

Regards,

Charles

 

L4 Prime for Advanced metering and Utilities

See Answer In Context

Reply
Replies 4
Charles_Murison
Picard Charles_Murison Picard
Picard

Posted: ‎2020-04-15 08:34 AM

0 Likes
0
698
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-04-15 08:34 AM

Hello @conradvr_hexeis ,

 

In the power meter module, the current and voltage value is the RMS over the entire 1 second interval.

 

Regards,

Charles

 

L4 Prime for Advanced metering and Utilities
Reply
DanL
Captain DanL Captain
Captain

Posted: ‎2020-04-15 10:54 AM . Last Modified: ‎2020-04-15 10:57 AM

0 Likes
2
693
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-04-15 10:54 AM

Hello Conrad,

Can you please describe or elaborate on the use case for the mean of the rms of previous 50 cycles of current?

I presume you you did not imply that the desired 1s value was the arithmetic mean of all instantaneous current (because this tends to 0A on all transformer coupled meters)?


As Charles indicates, the one second power meter module computes the RMS (aka. quadratic mean) of all cycles each second for voltage and current. The active and reactive power quantities are the (linear) arithmetic mean of power over 1 second.

 

Dan

Reply
conradvr_hexeis
Lieutenant | EcoXpert Master conradvr_hexeis Lieutenant | EcoXpert Master
Lieutenant | EcoXpert Master

Posted: ‎2020-04-15 06:43 PM

0 Likes
1
689
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-04-15 06:43 PM

Thanks David and Charles.  We needed to confirm that this was the RMS value over all cycles over the 1 second interval and not just the RMS value of the last cycle in the 1 second interval.

 

Correct I did not imply that this was the arithmetic mean of instant current values.

 

The use case is we are needing to plot a client's actual load at the 1 second point on a Time Rated Load Period Curve.

 

When using the high speed Power Meter module are the RMS values calculated on the last power cycle?

Reply
Charles_Murison
Picard Charles_Murison Picard
Picard

Posted: ‎2020-04-16 10:50 AM

1 Like
0
686
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-04-16 10:50 AM

Hello @conradvr_hexeis ,

 

The High speed Module is RMS for a full cycle updated every 1/2 cycle.

 

Charles

L4 Prime for Advanced metering and Utilities
Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Additional options
You do not have permission to remove this product association.
 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this forum after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2023 Schneider Electric, Inc